panel view 550
panel view 550
panel view 550
what causes error 32 at panelview 550 ab?
can solve this problem?
RE: panel view 550
What is the text that went along with the "error 32" message?
RE: panel view 550
Follow up:  According to the AB knowledgebase, self test 31 is for the real time clock.  If that failed on bootup, it's probably dead.
"On power-up, the PanelView terminal executes a series of self tests, below is a listing of the test number and the test functions..."
RE: panel view 550
panelview 550 displaying error 32 on power up (selp test)
i think error 31 is stuck key.
thanks
RE: panel view 550
            1  STATIC Ram Test
            2  Terminal Searching for a file to download
           10 Erase boot flash area.
           11 Copy boot code
           12 Boot code copy successful
           13 Boot code copy failed. check for error after boot code is copied to the onboard flash EPROM
           20 Erase firmware from flash EPROM
           21 Copy firmware to firmware flash memory
           22 Firmware copy successful
           23 Firmware copy failed
           24 Performed CRC base firmware check
           25 Firmware not compatible with boot code
           26 Firmware not compatible with hardware
           30 Watchdog test
           31 Stuck key test
           32 Real time clock test
           33 LCD RAM failed
           34 Performed CRC extended firmware check
NOTE: Not all of these test numbers are seen during a power up cycle
If a test fails, the terminal displays:
 ERROR!     FEHLER!     ERREUR!     ERRORE!
and the test #
RE: panel view 550
Forgot to mention, the above is from the AB online knowledgebase.
Syarifgemilang, you are correct, I meant to say error 32.
RE: panel view 550
Does the PV550 contain a battery-backed RTC? Often the RTC is combined with a small amount of RAM. Might be a fairly easy replacement, especially if this is one of the older PV550s. If it has a tungsten lamp instead of an LED backlight it is one of the earlier generation.
RE: panel view 550
Thank Kiljoy,ScottyUK
I am already learn more about this.
i found "led" red colour steady on... "Often the RTC is combined with a small amount of RAM" how to replace?
I am trial with other Circuit cat no:7753-702-52 it's ok
RE: panel view 550
I've never opened one up.