Current Transformer on both sides of the CB

Current Transformer on both sides of the CB

Current Transformer on both sides of the CB

(OP)
What is the advantage of having CTs on both sides of an outgoing feeder compared to CT on outgoing only with common CTs for busbar protection on the bus section.
Thanks in advance for help.

RE: Current Transformer on both sides of the CB

They may have different functions. Do you have a specific case in mind? What voltage level?

 

RE: Current Transformer on both sides of the CB

First, as long as the zones of protection overlap, it is fine. I have seen several industrial applications (5kV) that are configured with both CTs on the load side of the feeder breaker due to switchgear physical limitations.  

RE: Current Transformer on both sides of the CB

One is prob used for relay protection and the other for metering  

"Throughout space there is energy. Is this energy static or kinetic! If static our hopes are in vain; if kinetic — and this we know it is, for certain — then it is a mere question of time when men will succeed in attaching their machinery to the very wheelwork of nature". – Nikola Tesla
 

RE: Current Transformer on both sides of the CB

It is preferrable to have the CT for feeder protection on the bus side and the CT for bus protection on the line side.  This way, the breaker is in both zones of protection.

If the line is not a source, then there is no real increase in protection.  If there was a source on the line side and the line side protection trips the source, then a fault on the breaker would result in a trip of both sources to the fault.  This could be the case if there were differential or piloted protection on the line.

If both CTs were on the line side, then a breaker fault would not be in the line protection zone and fault clearing may be slower.
 

RE: Current Transformer on both sides of the CB

Hi.
Again to OP.
What is a voltage level? It's GIS or AIS?
I suggest it's HV level.
Please attach protection diagramm and we can talk about advantage and disadvantage of every case.
Best Regards.
Slava

"If both CTs were on the line side, then a breaker fault would not be in the line protection zone and fault clearing may be slower."
Jghrist, it's depend, CB protected by BBP (87B) and second zone of distance protection from opposite side or in case of OR zone with "zero" time
  

RE: Current Transformer on both sides of the CB

Note that on Cubicles 5A and 5B, both CTs are on the line side.  The protection is not shown on the new GIS, but it doesn't look like having both CTs on the line side of the new GIS will be a problem.  You could bid with an exception or figure out how much it will cost to make non-standard switchgear with CTs on each side and bid both ways.  Or ask the customer whether the exception would be acceptable.

RE: Current Transformer on both sides of the CB

Hi.
What Jghrist saied!!!
It's seems as standrd Siemens or ABB GIS ( AIS too), standard configuartion is CT on the line side, BTW on the bus-tie on the one side too. I don't see any protection problem, it's standrd 50/51 functionality, maybe with logical bus protection (recommended).
Good Luck.
Slava

RE: Current Transformer on both sides of the CB

(OP)
hi Jghrist
You are right, on 5A and 5B both CTs are on the line side, as per old specs. Now the new specs dictates to have CT's on both sides. I really dont have a clue what benefit it would give them.They are asking for Protection such as Directional phase overcurrent/earthfault protection and breaker failure on each breaker + high impedance busbar protection scheme with separate trip relays.
Cheers
thanks everyone for their valuable inputs

RE: Current Transformer on both sides of the CB

It is probable that one set of CTs are for Bus Differential protection and other is for the breaker overcurrent protection.

RE: Current Transformer on both sides of the CB

Hi.
Don't try understand, what is a benefit.
You have just provide all according spec. Don't try explain your opinion, isn't help.
Very simple logic, same was in old/exist open/air swg in another substations, it's all.

Good Luck.
Slava

 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources