Single Plate Connection Problem
Hi, I am using RAM Connection Standalone. I am designing a Single Plate Connection (Beam to Column Flange) .
The beam is a W16x36 and the column a W10 x 33, both ASTM 992 G50. The Ultimate Shear is 39.01K = (1.2*19.44)+(1.6*9.80)
The plate is A36, 9" length, 1/4" thick, vert & horiz edge dist = 1.5" and the vertical center-to-center distance= 3". The weld size is 3/16"
I am using 3 bolts (1 column, 3 rows).
When I look at the Design Report, all design checks are OK except in the "PLATE (support side)" section,
here, I get :
Weld Capacity 64.71k Demand 39.01K OK
Reduction Factor 1
Calculation Eccentricity (in) = 2.5"
Bending at Weld Line Capacity = 7.54 k.ft Demand = 8.13 k.ft NO GOOD
I have successfully checked all the results manually except the Bending at Weld Line Capacity.
How do I calculate by hand the "Bending at weld line capacity" (7.54 k.ft) for a quick check ?
What is the procedure ?
I have tried several ways but I come up with different results, not the 7.54 k.ft
Thank you,
DanteQ
here, I get :
Reduction Factor 1
Thank you,
DanteQ
RE: Single Plate Connection Problem
c and I are known. Make sure you use the h as the length of weld, b=.25 in. It sounds like you need to make the shear tab taller.
Never, but never question engineer's judgement
It's not the vector weld analysis kslee is suggesting. The 64.71k weld capacity corresponds to an instantaneous center of rotation capacity with e=2.5 in.
fa = 64.71/(9*.9) = 7.99
fv = 39.01/9 = 4.33
fb = sqr(7.99^2-4.33^2) = 6.72
M = 6.72*4.5*.5*6/12 = 7.56
If so what is the length of your horizontal welds?
0.08*E/Fy = 64.4
LTB will govern...
Iwx=d^3
vw=M*y/Iwx
But I figured it out. They're using the von-Mises shear reduction on page 10-103.
fv = 39.01/(9*.25) = 17.34 ksi
Fy = 36 ksi
Fcr = (Fy^2-3*fv^2)^0.5 = 19.85 ksi ***This equation is actually wrong***
phi = 0.9
Zx = 5.0625 in^3
phi Mn = phi Fcr Zx = 90.44 k-in = 7.54 k-ft.
*** The equation for Fcr is actually in error in the 13th edition manual. For LRFD, the equation should be:
phi Fcr = ((phi Fy)^2-3*fv^2)^0.5 = 12.16 ksi
phi Mn = phi Fcr Zx = 61.58 k-in = 5.13 k-ft, much less.
The example problems on the CD that came with the manual confirm the equation for phi Fcr above is the correct equation. See page IIA-58. The version in the seismic design manual, that includes the effects of axial load, is also incorrect. I've derived the equation, and agree with the example problem version. That is a whole other discussion, though.
Best regards.