Is it possible to calculate the surface temperature of boiler breeching with only the boiler flue temperature, the construction of the boiler breeching, and the ambient temperature?
The client has requested us to perform these calculations, but I dont think they have given us enough information.
The client has requested us to perform these calculations, but I dont think they have given us enough information.





RE: boiler breeching heat analysis
RE: boiler breeching heat analysis
RE: boiler breeching heat analysis
RE: boiler breeching heat analysis
the typical equations i have seen have you solving for the total heat flux given the interior and exterior surface temperatures, but in my case i only have the interior surface temperature. i have checked my heat transfer textbook but have so far been unable to figure this out.
RE: boiler breeching heat analysis
Given that plus what you have, work with a 1 degree temperature drop through the breeching system.
Maybe someone with more experience will jump in a suggest a better temperature drop, but solving for 1 will simply let you multiply later.
Flow rate x 1 degree x heat capacity = heat flux
That should get you to a single unknown to solve for.
RE: boiler breeching heat analysis
TTFN
FAQ731-376: Eng-Tips.com Forum Policies
RE: boiler breeching heat analysis
RE: boiler breeching heat analysis
rmw
RE: boiler breeching heat analysis
RE: boiler breeching heat analysis
RE: boiler breeching heat analysis
RE: boiler breeching heat analysis
You will also need to compute the inside film heat transfer coefficient , outside heat transfer coefficient ( which is combined effects of wind , natural convection, and radiation). The project spec should define the desing windspeed used for this calc if the flue is outdoors. One trick to help lower the surface temp for OSHA purposes ( for beaching that is within a distance that can be accessed by workers) is to use an anodized aluminum lagging; it has a emmissivigty of 0.95, compared to plain aluminum with an emmissivity of 0.10 .
RE: boiler breeching heat analysis
I admit to being very hesitant to answer questions in part because of your chosen handle. I certainly don't want to participate in sabotaging anything. You may wish to consider contacting the site management (either through the "Contact us" on the very bottom of the page or through use of a "red flag" on one of your posts) and requesting a name change. Your choice, obviously.
Patricia Lougheed
Please see FAQ731-376: Eng-Tips.com Forum Policies: Eng-Tips.com Forum Policies for tips on how to make the best use of the Eng-Tips Forums.
RE: boiler breeching heat analysis
that is exactly what i need to do, i need to show that the surface temperature of the flue will not cause any harm to workers or tenants. however as indicated by my first post and my subsequent attachment, i dont think the client has given me enough information to make this determination.
can i calculate the surface temperature with what i was given? if not, what other information would i need to get an answer? are there any spreadsheets or programs that makes this any easier? thanks in advance.
RE: boiler breeching heat analysis
q(btu/hr/ft2) = (Tg-Ta)/ R,total
R, total =sum{R1+R2+...}
R1= 1/h,i where h,i= inside film convective heat transfer coef for gas flowing inside the flue, from heat transfer text, or estimate as 7.0 btu/hr /ft2/F
R2= steel casing resistance to heat transfer = t/k (ft2-F-hr/btu) , t= thickness(ft) k= conductivity
R3= insulation resistance to heat transfer =t/k
R4= lagging resistance to conductionheat transfer =t/k
R5 = 1/(h,r+ h,c),, h,r= apparent radiation heat transfer coefficient = e*g*(Ts^4-Ta^4)/(Ts-Ta); iterative value, asume an initial value, solve the problem, then update estimate and solve again. e= lagging emissivity, see prior discussion a= 0.173E-8 btu/hr/ft2/R4, T in degrees rankine, H,c= outside film convective heat transfer coef due to either widnspeed or natural convection- see heat transfer text or use h,c=4. btu/hr/ft2/F Please note that it is easy to cheat by assuming a high e and a high H,c, so your ethics will be questioned if the client detects this.