Hello,
I'll preface this by saying that this is in one of our old powerplants, so it is exempt from the NEC but I do believe that we should adhere as much a possible.
I have found an installation of a feed from one panel to another, that welding cable was used. It is in steel conduit, is #1 copper, and operating at 480V.
If this was not in a powerplant, would this be allowed by NEC?
Thank you in advance.
I'll preface this by saying that this is in one of our old powerplants, so it is exempt from the NEC but I do believe that we should adhere as much a possible.
I have found an installation of a feed from one panel to another, that welding cable was used. It is in steel conduit, is #1 copper, and operating at 480V.
If this was not in a powerplant, would this be allowed by NEC?
Thank you in advance.






RE: Welding Cable
RE: Welding Cable
BUT for a Non-NEC power plant, have you considered locamotive cable? I saw it used in a small plant and started using it myself in small power plants. It is a tougher cable, both the insulation and the wire stranding and is available in much larger sizes than welding cable.
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: Welding Cable
RE: Welding Cable
That is, 353 MCM is a tight fit in 500 MCM connectors.
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: Welding Cable
One feature of loco-power cable is that it is readily available as (UL) RHH/RHW, satisfying the code aspect. It's stranding is much finer than the usual "building wire", i.e., more flexible, but is not as fine as welding cable.
htt
or Google 'locomotive cable RHW'.