What contractor will prefer?

What contractor will prefer?

What contractor will prefer?

(OP)
I have a 7 feet wide wall footing. Wall is 18 inch wide and footing is 18 inch deep (thick). It has rebars #5 @ 12 " c/c Top & Bottom  E.W (EACH WAY).
I checked I do not need to bend rebars at ends to attain development length. Most likely will contractor will go with plastic chairs or will like to bend it at ends
to give support to top mesh from bottom mesh?
 

RE: What contractor will prefer?

You won't find chairs tall enough for your top bars.  It's easier for the contractor to use bent bars and ties to hold the rebar cage together.

Bottom mat will likely be supported on concrete bricks.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources