Does a fixture need to be de-energized merely to replace a lamp? (assume HID hi-bay for now)

Is de-energization only applicable if the the work would involve exposing live conductors?...such as in a ballast replacement, etc...

RE: Lamp Replacement

Short answer, yes.

RE: Lamp Replacement

(OP)
What's the medium or long answer? smile

It appears to be do-able from looking at OSHA 1910.333(a)(1) & 1910.333(a)(1) if I have qualified people and proper techniques, tools, etc.

I was curious if anyone had direct experience with this issue. We will likely require de-energizing first as a rule, but I would be willing to bet that most would replace a burnt out (cold) lamp without caring too much about whether the fixture is on or off...and I am not convinced about there being any perceptible risk... (until the one time in a trillion that something bad would happen...)

Some lamp manufacturer's say to de-energize, not sure if the ballast or fixture manufacturer's state anything.

Is there an OSHA anonymous hotline? smile

RE: Lamp Replacement

OK, not quite as short answer, refer to the 2009 NFPA 70E, where you will find what it takes to do energized work.

Medium answer, either you have to justify the energized work because denergizing poses a greater threat to safety than working live (Good luck because they used to have "removal of illumination from an area" as a justifiable reason and removed that in the most recent edition), and even if you can justify it you need to fill out an Energized Electrical Work Permit, including the risk analysis. Or, you can denergize it.

Dont make me post the long answer.

And yes, you can write a letter to OSHA asking anything and get a letter of interpration on the topic. They enforce the 70E as a industry standard through the general duty clause.  

RE: Lamp Replacement

The medium answer is that changing the bulbs presents a hazard from exposed live electrical connections in direct proximity to the person whom is performing the work.  The other concern is the possibiliy for the bulb to explode from the sudden flow of current, and if the technician doesn't get a good connection there is also a potential for arcing.  

OSHA's standard for electrical safety has always been a slippery slope in that it is very ambiguous and references a lot of other standards (NFPA 70E, NEC, etc.)  Best practice is to perform the work de-energized.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources