Turbo Generator Water Chemistry
Turbo Generator Water Chemistry
(OP)
Hi
A question below:
1. what are the advantages of operating stator water chemisty at low oxyen elevated PH. I recently experienced high copper from the water, oxygen, ph, conductivity levels all ok. iron slightly out.
2. what is the safest dew point when operating h2-water cooled machine? is dew point based on stator water temps?
3. What impact will generator that is designed to operate at 40 deg.cel inlet stator water and then inlet temperature is decreased to 35 de.cel. Ambient temp is normally at 36 deg.cel.
4. When doing on line monitoring on one of the units, i saw partial discharge increasing to high values and coming from the line terminal bushing chamber, what could be the source, some suggested CTs but no volatge on the CT as far as i know, bushings were cleaned off contaminations.
Please advice.
A question below:
1. what are the advantages of operating stator water chemisty at low oxyen elevated PH. I recently experienced high copper from the water, oxygen, ph, conductivity levels all ok. iron slightly out.
2. what is the safest dew point when operating h2-water cooled machine? is dew point based on stator water temps?
3. What impact will generator that is designed to operate at 40 deg.cel inlet stator water and then inlet temperature is decreased to 35 de.cel. Ambient temp is normally at 36 deg.cel.
4. When doing on line monitoring on one of the units, i saw partial discharge increasing to high values and coming from the line terminal bushing chamber, what could be the source, some suggested CTs but no volatge on the CT as far as i know, bushings were cleaned off contaminations.
Please advice.






RE: Turbo Generator Water Chemistry
Bekza:
Cooling water with a pH of 8.5 to 9 has the advantage that the formation of copper oxide products is reduced to a minimum. This in turn is minimizing possible clogging of hollow conductors. Only one generator manufacturer is sucessfully implementing this elevated pH technique. Just ask the supplier of your generator.
A sudden high copper level in the cooling water system means that you disturbed the water chemistry. Don't play around with the system by experimenting and taking an excessive number of water samples. Leave the system alone.
What you mean with "iron slightly out"?
An ambient temperature of 36 degrees C is irrelevant for a H2 cooled generator. Its the hydrogen temperature inside the generator that counts.
Regards
Wolf
www.hydropower-consult.com