General VFD Question

General VFD Question

General VFD Question

(OP)
General question regarding PWM VFD (inverter)operation.  Using the constant torque setting (V/f), does the input current of the inverter increase as the output frequency increases? and if so, then is it proportional to the output frequency?

RE: General VFD Question

Drive output kva has to be supplied from input kva.  Thus, there is no correlation between output frequency and input amps.  Since input voltage is nearly constant, you could expect input amps to rise and fall in fairly close relationship to output load.

RE: General VFD Question

Using the constant torque setting (V/f), does the input current of the inverter increase as the output frequency increases?
It may but this depends on having a true constant torque load rather than the VFD setting.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: General VFD Question

If your output current is constant with changing frequency, and the drive has a constant V/F, then the input current will increase linearly with frequency (in theory).
As DickDV stated above, the output VA is supplied by the input VA and as the voltage on the output changes, the ratio of input to output voltage changes, so the ratio of the currents must also change to keep the input VA almost equal to the output VA.

With a vector drive or a drive that does not have a constant V/F, the output voltage still changes with frequency, but not in a linear fashion, so the input current still changes with frequency, but not linearly.

Best regards,
Mark.

Mark Empson
L M Photonics Ltd

RE: General VFD Question

Dick,

Can I politely disagree with you, on choice of terminology at least? Input kW and output kW have a definite relationship with the difference being the drive losses, but input and output kVAr aren't so closely related as one depends on the motor magnetic design and the other depends on the front end rectfier, and by implication the input and output kVA have a less obvious relationship. I know you know that I know that you know. smile
  

----------------------------------
  
If we learn from our mistakes I'm getting a great education!
 

RE: General VFD Question

I used the term "kva" because of the non-linear waveforms at both input and output but I suppose "kw" would be more precise. In fact, I hardly gave it any thought!  Probably should have!

Thanks for the correction,  DickDV

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources