Mesh as Shear Reinforcement for Beams / Development
Mesh as Shear Reinforcement for Beams / Development
(OP)
Hi All,
Does anyone have experience in using mesh as shear reinforcement for beams?
The Australian code AS3600 requires the wire ends to be hooked or to have 2 of the transverse wires in the compression zone.
The main problem I am having is my compression zone is only 100mm (4") from the top of the beam - meaning technically 'no' anchorage.
Could you consider that having one bar in the compression zone is 50 % developed and hence half the shear strength?
I'd also like to know what other codes stipulate.
Cheers.
Does anyone have experience in using mesh as shear reinforcement for beams?
The Australian code AS3600 requires the wire ends to be hooked or to have 2 of the transverse wires in the compression zone.
The main problem I am having is my compression zone is only 100mm (4") from the top of the beam - meaning technically 'no' anchorage.
Could you consider that having one bar in the compression zone is 50 % developed and hence half the shear strength?
I'd also like to know what other codes stipulate.
Cheers.






RE: Mesh as Shear Reinforcement for Beams / Development
h
RE: Mesh as Shear Reinforcement for Beams / Development
Thanks for that. The info appears to cover the steel shear capacity of the mesh itself.
I'd be interested to know if there are papers on beam shear tests with mesh as reinforcement.
Cheers
RE: Mesh as Shear Reinforcement for Beams / Development
The code provision is based on the fact that it takes 2 transverse bars to take the load. Looks like you are right about the 50% check out page 56 of the following link:
http://w
Mesh is really only useful if you have a deep beam as the compression region is actually deeper than the classical limit states formula.
RE: Mesh as Shear Reinforcement for Beams / Development
Dik