Two 11 KV Incomers
3

Two 11 KV Incomers

Two 11 KV Incomers

(OP)
What may be the reasons why two 11 KV incomers can not be paralleled?  

RE: Two 11 KV Incomers

Mostly because they weren't designed to be parallel.  Lots and lots of reasons, but no idea which might apply to your situation due to a lack of detail in your question.

RE: Two 11 KV Incomers

The voltages may have different phase angles.  They may come from different sources and paralleling the incomers could cause undesirable circulating currents between the sources.
 

RE: Two 11 KV Incomers

Additional option:
Level of SC in case of paralleling is more then capability of SWG.
Best Regards.
Slava

RE: Two 11 KV Incomers

Circulating currents in the supply source?

RE: Two 11 KV Incomers

emillar:
There may be non-technical reasons, such as safety. As davidbeach indicated you haven't provided enough detail about your situation to respond properly.

 

RE: Two 11 KV Incomers

with 11kv you need to check your sequence and connections, Your rotation may be the same on both supplies but the sequence may be out. ie. A-B-C and B-C-A on the other feeder. trying to connect those and you would have an issue.

Are the 11kv Supplies from the same source ? Not a generator and utility supply?

fault levels may be significantly changed by paralleling up two supplies enought that it would exceed that could be safely handled by the fitted protection.

It is however common to allow parallel operation during switching to prevent loss of power but this is done carefully and under the instruction of the supply company and generally involves a very short duration of time that the two supplies are run in unison.

RE: Two 11 KV Incomers

By paralelling the 2 sources you may have available fault currents thayt exceed the AIC ratings of your switchgear. Thats bad mamma jamma.  

RE: Two 11 KV Incomers

Yep well put bad mamma jamma

 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources