Ungrounded power TR in grounded network
3

Ungrounded power TR in grounded network

Ungrounded power TR in grounded network

(OP)
Our contractor wants to install power transformer 110/20/6kV, Y,yn9,d11 in a substation. Primary (110kV) wounding of TR is not grounded. 110kV network is directly grounded.

Whats are the consequncies of connecting ungrouded primary in grounded network?

RE: Ungrounded power TR in grounded network

Hi.
Actually isn't problem, but you must check with your utilities. Point is, a ground fault level in this area.
For example only now, we installed two trafos 45/63MVA Y is ungrounded in 170kV grounded network. Reason is , installation is near ( 200-300m) to four big GSU ( 400 MVA) trafos.
Good Luck.
Slava

RE: Ungrounded power TR in grounded network

2
Make sure the transformer is specified correctly as the primary insulation may be graded towards the star point if its designed for a grounded system.
Regards
Marmite

RE: Ungrounded power TR in grounded network

(OP)
If i got this clear. Ground fault on one phase couses overvoltages in other two phases and in isolated star point. So I need higher insulation level on TR and on switchgear?

RE: Ungrounded power TR in grounded network

Hi Mirilovic .
Star point is isolated, is true. But grid is directly grounded.
You haven't overvoltages in case of ground fault. Of course if you haven't some islanding mode or your trafo is GSU.
Best Regards.
Slava

RE: Ungrounded power TR in grounded network

In the design of the transformer and substation was there a fault current study done? Where do you want the zero sequence currents to go.  Typically protection engineers like to see the zero sequence currents return to the source transformers of the system, not to through the load transformers.  By not grounding the Star Point of a Wye connected windings or using a delta connected system you eliminate the zero sequence path.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources