Gents,

I know the system criticality plays a big roll here to design the valve with Bypass or Hand jack. But, does any one have tips or criteria to help for designing the Valves with bypass or Hand jack?

Thanks and Regards
TH
 
 

RE: Bypass or Hand jack

(OP)
does any one have tips or criteria to help for designing the Valves with bypass or Hand jack rather than criticality?
 

RE: Bypass or Hand jack

Besides corporate standards, several factors can affect the decision to provide a control valve with a bypass or handwheel.

Onshore plants are less concerned about weight than offshore.  Offshore may use few bypass valves; many bypass valves are used in similar onshore applications.

Lacking blocks and bypass you cannot service the control valve.  If critical for operation you need the ability to service the control valve.  Sometimes, parallel control valves with block valves are used in lieu of a bypass.

Modular packages permit taking a portion of the process down and operate at reduced rates.  This permits servicing a control valve with neither a bypass or handwheel.

RE: Bypass or Hand jack

Are you talking about putting a hand wheel on bypass valve with an operator to use if the operator fails?

Some of our high pressure motorized steam bypass valves have hand wheels on the valves operator in case of valve operator failure. I can only recall one time that a bypass valve was operated with the hand wheel. It didn't take the mechanics too long to replace the faulty operator as they had to help operate the 24" valve using the hand wheel.   

RE: Bypass or Hand jack

thalathb,
Another factor is size of control valve.  As the control valve size increases, so does the size of the manual bypass valve and the size of the manual isolation valves around the control valve set.  Larger size means more space required and more cost so larger sizes start to cause layout and financial worries.  For onshore installations, design contractors tend to have size limits of between 8" and 12" where they deem a bypass valve to be impractical.

RE: Bypass or Hand jack

(OP)
Thanks all for your inputs.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources