Synch check

Synch check

Synch check

(OP)
In case when line is energize but bus is dead..whether synch check will be completed with dead bus and live line ?
Do CB closes in this condition?

RE: Synch check

it will if your synch check is set to allow it.  Check the settings.

RE: Synch check

You really should consider some interlocking so that 'dead bus' is not a condition which can accidentally occur because someone left the VTs isolated.
  

----------------------------------
  
If we learn from our mistakes I'm getting a great education!
 

RE: Synch check

Hi.
In case of voltagecheck ( live-dead or dead-dead) as Scotty saied you have check additional criterions as :
1. MCB (fuses) OK
2. All other feedeng breakers are opened.
Best Regards.
Slava

RE: Synch check

Permissive to close on a dead bus is a separate logic from the Synch check. Since synch check permissive contact will not close with a dead bus (as there is no synch) you need either a hardwired or software (if programmable) logic to bypass the synch check relay on a dead bus. You also need to have a logic in place that prevents closing on a dead bus which is dead because of a fault! If any of the source breakers have a bell alarm (open due to overcurrents) you need to lock out the bus.

 

RE: Synch check

Hello.
Newer synchrocheck relays are include voltagecheck option too.
Usually is include some binary input: dead bus (DB)release.
Possible add to this contact any logic.
In case of protection operated, latch contact add directly (in series) to the close coil. Ofcourse in case of autoreclosere functionality only afterfinally trip.
Best Regards.
Slava

RE: Synch check

Of course - u can close CB. How could u energize S/S (bus bar) if u don't close breaker?
You can choose - if it is request of Grid department, than through Sync logic - close CB when:
DL-DB
DL-LB
LL-DB
LL-LB (volt, angle, freq condition - are in setting region)

(AND if no VT MCB trip, interlock, voltage not in DEAD zone - conditions are fulfilled)
 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources