aircooled chiller & water cooled chiller performance /derating

aircooled chiller & water cooled chiller performance /derating

aircooled chiller & water cooled chiller performance /derating

(OP)
Dear member,
   i wish to know the performance of  aircooled chiller & water cooled chiller  when the  opearting condition is  different from the design condition.
(i.e) when the dry bulb(air cooled) or wet bulb( water cooled chiller) is different from the design  condition.
 also what will be  the impact when the  aircooled chiller  condensing coil is choked(dirt deposit) or not maintained properly.
 is there any graph  or article explaining this  query in details.
 

RE: aircooled chiller & water cooled chiller performance /derating

The chiller catalog should have correction factors for different outside air temperatures.

When the condensing coils are clogged, performance goes right into the dirt.  The unit will probably shut off due to high head pressure (refrigerant is not condensing).

When the unit is not maintained properly, performance also goes right into the dirt and can result in expen$ive repairs.

 

RE: aircooled chiller & water cooled chiller performance /derating

(OP)
Dear members,
 i came to know about this. is there any illustrative examples or articles regarding this.

A dirty condenser coil that raises condensing temperature from 95°F to 105°F cuts cooling capacity by 7 percent and increases power consumption by 10 percent, with a net (compressor) efficiency reduction of 16 percent

RE: aircooled chiller & water cooled chiller performance /derating

If you want to deep dive into this: look up the recent ASHRAE research project RP 1275 Final Report.  It'll tell you more than you ever wanted to know about the relative effects of faults on chillers.

ASHRAE technical committee TC 7.5 has churned out a tonne of fault diagnostic related studies.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources