Acceptance Testing on 33/11 Transformer

Acceptance Testing on 33/11 Transformer

Acceptance Testing on 33/11 Transformer

(OP)
Hi all, im looking for some information on acceptance testing of a 33/11 15MVA transformer. Most of all im looking for the IEC testing standard for this work and what tests other people carry out.
Thanks Heaps
Michael

RE: Acceptance Testing on 33/11 Transformer

dotdognz

IEC 60076-1 is the IEC standard for testing of power transformers.   It states the type and routine tests required in the factory.

My assumption is that you are talking about testing of your transformer on site prior to commissioning.  If this is the case, then you can reasonably do a cut down set of  tests that were performed in the factory.

A list of tests that we perform are:
insulation resistance
induced voltage test
applied voltage test
ratio
winding resistance
frequency response
partial discharge and power factor of bushings (if >33kV)
full suite of oil tests prior to commissioning

This list is by no means exhaustive, however we find that these tests give us confidence that the transformer was delivery to site in good condition, is ready for service, and we have a good set of benchmark figure for down the track if there is a failure or if we are concerned about the number of through faults the transformer has seen.

Other companies may also perform:
leakage reactance
power factor measurements on the winding insulation
polarisation/depolarisation current measurement *
recovery voltage measurement *
frequency domain spectroscopy measurements *
infra-red scan of the transformer and bushing connections after commissioning

* these 3 measurement techniques provide an indication of the quality of the insulation, and how much moisture is in the windings.  we use this down the track, as we have the assumption (backed up by oil tests for moisture content) that the insulation is dry for a start, so we would be getting an almost perfect curve).


ausphil.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources