577 volts to 480volts?

577 volts to 480volts?

577 volts to 480volts?

(OP)
We are running 480 volt 3 pahse at our facility. We found a deal on a piece of equitment we need,but the motor is wound for 577 volts. Would it be alright to run this motor at 480 volts and expecting slightly more amp draw?

RE: 577 volts to 480volts?

Probably not.  That's a big difference in voltage.  

If you are getting such a good deal, you'll be able to buy an autotransformer with all that extra money and boost the voltage up to what it should be.  



 

RE: 577 volts to 480volts?

(OP)
Yea ,I could do that but I have a very small inside cabinet that is aleady loaded with no room. Besides that everything else is 480 volts so it might confuse someone after me, especially if a nameplate got to missing. If it would be a big problem I would just have the motor rewound. Thanks for the reply.

RE: 577 volts to 480volts?

The autotransformer is a good solution - much less costly than trying to rewind the motor.  But whatever you think.

Pretty sure you won't be happy running the 577 V motor at 480 V.  

RE: 577 volts to 480volts?

Post the motor rated Full Load Amps at 577 Volts and we can show you a sample transformer size. The transformers may be much smaller than you suspect. I have encountered this issue a lot. I typically mount the transformers close to the motor. Is this a 60 Hz motor?  

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: 577 volts to 480volts?

  
      
Every time you ask something about motors, you need to write all the details from the nameplate..
Zlatkodo

RE: 577 volts to 480volts?

It will be cheaper to rewind that motor to 480 V.  

RE: 577 volts to 480volts?

Sample calculation;
Motor current = 5 Amps
Boost needed = 120 volts
KVA = 5A x 120V / 1000 = 0.6 KVA
For this example motor you would need 2 boost rated 480:120 Volt transformers connected in open delta auto-transformer boost configuration. Dry type transformers may be mounted outside a panel or control enclosure. I have mounted them on the floor beside the motor at times.
 

Bill
--------------------
"Why not the best?"
Jimmy Carter

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources