Hi guys.
One of the things we run into often when doing a revamp is the need to recalibrate the instruments; Temperature, Pressure instruments as well as Level instruments.

My question is why do we need to calibrate an existing instrument?
For example, suppose we are changing the operating condition of an existing tower from 25 Barg to 20 barg..Would there be a need to recalibrate the pressure instrument? Why?

Thanks
 

RE: Instrument Calibration

Regardless of changing operating pressure or service all instruments should be on some type of preventive program to periodically recalibrate as much as possible.    And if a unit has been down for some time all instrumentation should be checked before restarting. This is just good engineering practice.

RE: Instrument Calibration

Consider instrument validation instead of calibration.  The calibration for the latest series of electronic transmitters stays very solid.  Range changes can be done with a hand held communicator.  It is always a good practice to validate (applying pressure etc.) to assure that the transmitter is working, and to verify that the transmitter range matches the display range.

RE: Instrument Calibration

Older instruments with screws for zero and range will wander around a bit.  You need to dial them back in on a test bench.  Definitely loop test as part of Commissioning.

In your 25bar changing to 20bar example - You choke the resolution of the control loop down into 80% of the full range.  Might mess with the loop gain too.  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources