The National Electrical Code (NEC) has a 6' vertical clearance requirement above electrical equipment (panelboards and switchboards) where no "foreign" equipment (ductwork, piping, etc.) can be installed. This requirement is for low voltage systems , 600v and below.

I An inspector told me that the 6' is in place because to keep stray voltages from energizing metallic objectives such as ductwork or  piping. I find this hard to believe. You would need a "stray" current first to produce a "stray" voltage.

Yes, you could get a stray current from the magnetic fields from transformers, and perhaps from feeders that are unbalanced. But i just don't see ductwork and piping getting energized from nearby.

Anyone know where i might find some source of information where studies have been performed on this?

Thanks in advance.

b

RE: The NEC, stray voltage, and ductwork

Nothing to do with stray voltages i don't think.  It's just to allow adequate space above for getting conduits in and allowing some working space.  The panels are enclosed in a grounded enclosure, so electric field effect is minimal.   
 

RE: The NEC, stray voltage, and ductwork

I'm with dpc on this. Remember, even the best and most knowledgeable inspector does not know everything.
In Canada I check the Handbook to The Canadian Electrical Code for an authoritative answer to questions about the "Why" behind code rules. I don't have access to my copy just now. Is there an equivalent handbook for the NEC?.  

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: The NEC, stray voltage, and ductwork

Bill,

Yes there are at least a couple.  The one published by NFPA - the NEC Handbook is a good resource and also includes the entire text of the NEC.   

RE: The NEC, stray voltage, and ductwork

You can check it; measure open circuit on ductwork with respect to ground, then lay a live insulated conductor on the ductwork and repeat.

If there is any AC/DC voltage at all, load it with 1, 10 or 100 ohm resistors and figure out the Thevenin equiv. source impedance.

There might be 100 pF/foot of capacitance between Romex and the ductwork.

RE: The NEC, stray voltage, and ductwork

I guess this has to do with NEC 110.26(F)(1)(a).

Our 2008 NEC Handbook explains, "This reserved space permits busways, conduits, raceways, and cables to enter the equipment," which confirms dpc's explanation.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources