Concrete Precast Double Tees

Concrete Precast Double Tees

Concrete Precast Double Tees

(OP)
Does anyone know where i can find load tables for precast double tess from the late 60's ealry 70's?  I'm trying to evaluate a roof and walls that used these as the structural elements.

RE: Concrete Precast Double Tees

try contacting a local supplier.

RE: Concrete Precast Double Tees

There's load tables in the PCI Design Handbook, second edition, from that era.  Unfortunately, for any one size of double tee, there's several capacities dependent on the amount of prestressing. I'm not even sure you can conservatively assume the lowest values, as the double tees were usually designed for specific loads given by the designer.  
If you're very lucky maybe the company that produced them still has records.  But that's not very likely. Do you have the design documents? They should indicate floor and roof loading.

RE: Concrete Precast Double Tees

I have some charts if you want to email me- I can send them to you.
geoff@redaleltd.ca

RE: Concrete Precast Double Tees

(OP)
Thanks for all your help everyone!  I hope I can reture the favor.  The roof loading is indicated, but I think they were way overdesigned.  They are 8' wide (stems @ 4') at 18-1/2" deep total (16" stems + 2-1/2" slab).  The span is only 19'-8".  The snow load is only 37 psf, but they have added a bunch aof roof top units.  i'm trying to get a sense of how much load they can handle for that span.  I'm looking to be very conservative...........

RE: Concrete Precast Double Tees

It is a function of the number, location and size of stressed strands.

RE: Concrete Precast Double Tees

Instead of guessing around precast/prestressed concrete structures, have you checked to see if there exist possibilities to bring the load of new roof top additions to the end bearing such as adding elevated steel framing.

RE: Concrete Precast Double Tees

Sounds relatively conservative, but maybe to be sure, look at some x ray testing to see the strand size and spacing?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources