Convert cv to cg
Convert cv to cg
Can anyone help....
How do convert cv to cg ?
I know that cv = constant x kg
Cv [US Gallons/min/psi] = 0,03445 KG [m³/h/bar] (related to natural gas, density = 0,83 kg/m³) ( by manufacture)
Note: But the service that valve is for H2. Is valid the same relation or the constant is different ??.
Thanks.
Thanks.
RE: Convert cv to cg
Divide by the specific gravity of your gas to adjust for gases other than air.
"Pumping accounts for 20% of the world's energy used by electric motors and 25-50% of the total electrical energy usage in certain industrial facilities."-DOE statistic (Note: Make that 99% for pipeline companies) http://virtualpipeline.spaces.live.com/
(densidade = 14,55 kg/m3 ; Z=1,084; cp/cv =1,45)
cv ou kv ?? please is urgent
considering :
C1=39.76*(Xt)^0.5
"Xt ???"
I should have clairified. This formula is from Fisher Control Valve. Xt is another coefficient they assumed we needed.
How??
As said, Cg = C1 * Cv.
I'll typically look up the C1 as it varies depending on the type of control valve, conventional style globe valves are usually around 30 but it can be quite a bit lower
If you can clarify what you want it would help, the hydrogen conditions by itself doesn't have anything to do with the Cv or Cg.
I clipped this from the bottom of one of Fisher's coefficient's pages. It is in each of their control valve pdf files.
Conversion of Sizing Coefficients
Following are conversions for use with other common sizing equations.
Kv = (0.865)Cv
C1= 39.76(XT)^0.5
Cg = CvC1
Km = FL^2
Cs = 1/20(Cg). Cs is only applicable for inlet pressures up to 70 bar(a)
psafety
ht