Injection System spacing

Injection System spacing

RE: Injection System spacing

Can anyone give me info on how injection/rejection works?

RE: Injection System spacing

I don't know that there is any typical spacing versus pipe diameter.  

...which may be the reason that no one else has answered as well.

Patricia Lougheed

Please see FAQ731-376: Eng-Tips.com Forum Policies: Eng-Tips.com Forum Policies for tips on how to make the best use of the Eng-Tips Forums.

RE: Injection System spacing

Maximum spacing between the tees should be less than 4x the pipe diameter of the primary pipe in order to minimize the pressure drop between the supply and return tees. You want to minimize the pressure drop to hydraulically separate the injection pump system from the primary system.

John Siegenthaler has some great articles on hydronic system design.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources