Masonry Horizontal Joint Reinforcing.

Masonry Horizontal Joint Reinforcing.

Masonry Horizontal Joint Reinforcing.

(OP)
When using a #9 Dur-O-Wall horizontal joint reinforcing at 16" o.c.  What are the requirements for lapping this type of reinforcing at the corners?  Is the mason supposed to buy a prefabricated corner section to use in these locations or is lapping allowed?

I can't seem to find any requirement in ACI 530.1.
 

RE: Masonry Horizontal Joint Reinforcing.

With the ladder type, I generally lap it 'one rung' <G>.  I seem to recall Dur-o-wal has a discription of the splicing.

Dik

RE: Masonry Horizontal Joint Reinforcing.

Lap ends of reinforcement 6". It is common to cut the interior wire and field bend the continuous reinforcement at corners.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources