Contactor Overload Trip Curves

Contactor Overload Trip Curves

Contactor Overload Trip Curves

(OP)
Do contactor thermal overloads have the same type of trip curve characteristics as circuit breakers. And if so, how do you specify this, and is this information generally printed on overload labels??

RE: Contactor Overload Trip Curves

No. Thermal overload relays are listed as Class 10, Class 15, Class 20 and Class 30. The number relates to the tripping time at 6x setting. Most manufacturers publish the standard curves. I'm not sure which standard defines them - I'll have a look at work when I get there.
  

----------------------------------
  
If we learn from our mistakes I'm getting a great education!
 

RE: Contactor Overload Trip Curves

In the US, the standard is carried by UL now under UL508 although originally it was NEMA standard ICS-2 (but NEMA is not an approval or testing agency, hence the adoption by UL). For IEC, it is IEC 947-4-1. They are not exactly the same, but close enough not to worry about the differences.


"If I had eight hours to chop down a tree, I'd spend six sharpening my axe." -- Abraham Lincoln  
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies  

RE: Contactor Overload Trip Curves

Thanks jraef.
  

----------------------------------
  
If we learn from our mistakes I'm getting a great education!
 

RE: Contactor Overload Trip Curves

(OP)
Thankyou both very much,

RE: Contactor Overload Trip Curves

You can use an I^2*T curve wiht the "class" as the tripping time at 600% of rated current.  It won't be exact, but it'll be close enough.  If you're coordinating closer than the accuracy this statement produces, you're doing it wrong.

old field guy

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources