Torsion on LVL beam supporting brick
2

Torsion on LVL beam supporting brick

Torsion on LVL beam supporting brick

(OP)
I recently did an inspection on an 18 ft span beam lintel, most likely made of an LVL beam (Drywall is still in place). The beam is supporting half of a 2nd story, roof and brick. The brick is supported on a steel angle which in turn is bolted to the LVL beam. The beam is currently at a deflection of L/300 and the brick facade has cracked. There is also slight twist of the steel angle.

The questions are:
1) Is it allowed by code to support brick with a Pre-engineered wood beam? (Despite the fact that the criteria of L/600 deflection is respected). I could not locate on IBC2006 were this is addressed.

2) Do you have a good reference on calculating strength of a wood beam due to excentric loading, such as brick?

3) In repairing the beam, should we simply replace the wood with a steel tube beam, which then would require steel columns...

Any comments would be appreciated. Thanks,

ST

RE: Torsion on LVL beam supporting brick

No, brick can not be supported by a combustible material (including wood).  This was often done at setback gable roofs where the lintel was bolted to the bottom chord of the gable truss.  This violates the IBC.

RE: Torsion on LVL beam supporting brick

R703.7.3  Masonry veneer above openings shall be non-combustible

RE: Torsion on LVL beam supporting brick

(OP)
So, no LVL beam is allowed at all on residential, to support brick? I suppose the steel angle would have to be designed so it is self supporting (i.e. not attached to the LVL)????
A fire treated wood would then be allowed?

RE: Torsion on LVL beam supporting brick

In response to your question 2, I have designed LVL lintels to support brick veneer.  More correctly, I have used PSL lintels, because they come in a 5.25" width.

The torsion on a rectangular shape = cM/At, where c is a coefficient which depends on the aspect ratio of the rectangle, M is the torsional moment, A is the area of the rectangle, and t is the length of the smaller side of the rectangle.  This shear stress is added to the shear stress due to direct shear, and the total shear stress is compared to the allowable shear stress (for example, 290 psi for PSL).

But I have found the difficult part of designing a header for torsion is the end connection.  Usually, several lag screws are required to transfer the torsion from the header to the king stud.

DaveAtkins

RE: Torsion on LVL beam supporting brick

Dave has nailed the answer.  Look closely at the end connection.  The torsion has to be developed.

RE: Torsion on LVL beam supporting brick

(OP)
So the question is, from a Code point of view, is it allowed to use a PSL? How did you justify using a PSL vs the fact that combustible material is not allowed as lintel material?

RE: Torsion on LVL beam supporting brick

There is nothing in the IBC that I can see that prevents masonry from being supported on a steel ledge angle which is bolted to an LVL beam.  (except fireplace mansonry)   Solid blocking at the ends of an LVL lintel should be provided regardless of whether the LVL is eccentrically loaded or not.  Torsional restraint at the ends of beam can be easily resolved into a force couple at the top and bottom of beam. Blocking may be evaluated based on the calculated restraint force.

One caveat is that there are LVL manufacturer recommendations that there be a moisture barrier between the masonry mortar and LVL.  I suppose this is to prevent degradation of wood fiber and lamination bond at the point of bearing.

Hope this is helpful.

RE: Torsion on LVL beam supporting brick

(OP)
Lobstateata, that is what I was inclined in believing, but I could never find anyone to point out clearly an answer.

So, do you all know how to evaluate the torsional deflection resulting on a wood or PSL beam?

RE: Torsion on LVL beam supporting brick

By torsional deflection, I assume you are referring to the resulting rotation at mid-span?  Torsional stresses due to warping requires information about the full length of the member, the boundary conditions on the member and the variation of loading along the length of the member, as outlined by Dave above.


Try the following link for a basic treatise on the subject.

http://www.ae.msstate.edu/~masoud/Teaching/SA2/chA6.4_text.html
 

RE: Torsion on LVL beam supporting brick

Wait a minute - keep in mind that the IBC doesn't apply here.

This is a residential house - therefore IRC applies.  Also, the IRC allows brick veneer to be supported on steel angles attached to wood studs for instance (see Figure R703.7.2.1).

Supporting from a PSL (LVL or other) composite lumber should be OK provided the following:

1.  The wood beam is designed for long term deflections and limited to L/600 or 0.3" (per ACI 530).  

2.  The brick sits directly on a steel angle and not on the wood itself.

3.  The resulting torsion is taken into account (per DaveAtkins above)...and also considered for the design of the supporting end posts.

 

RE: Torsion on LVL beam supporting brick


Quite right about using IRC JAE.  My mistake.

RE: Torsion on LVL beam supporting brick

structurebeton,

In trying to calculate the expected rotation of the beam, remember that it is a summation of the amount the beam twists between the supports and the amount the ends rotate due to bending of the supporting posts.  You can probably get a good idea of which component is most important by observing the way the brick is cracked.   

RE: Torsion on LVL beam supporting brick

(OP)
There is one vertical crack right in the middle of the span, and one diagonal crack on the right corner, and another diagonal crack on the left corner, higher on the wall. It clearly shows a failure due to bending of the beam, but it could also show failure due to torsional stress.

RE: Torsion on LVL beam supporting brick

My guess is the supports have rotated.  Be careful, because if that is the issue, the whole thing could suddenly collapse.

RE: Torsion on LVL beam supporting brick

Thanks for the photos.  I would tend to agree that it is not about to fall down.  Probably has somehow achieved equilibrium.

I think you have to now remove the interior finish from the beam enough to expose the beam section, the end connections, and the connections of the shelf angle.

You said the deflection is L/300, so it looks like that is around 20 mm.  Certainly enough to cause the cracking without any accompanying rotation, as there are no vertical control joints.

Part of the shelf angle deflection could be differential to the beam deflection, depending on the connection between the two.

RE: Torsion on LVL beam supporting brick

Rather than taking out the torsion at the end of the beam, if it is possible, I would remove the torsional rotation  with diagonal struts back to the floor diaphragm from the top and bottom of the beam at regular ingervals along the length.  This could be accomplished with tension strap connector ties and diagonal compression members.  

And, yes, I have a 24" deep brick fascade over my garage doors that is supported on 12" deep wood headers and 4x4 steel angles, but no kickers.  I have no structural problems, but the span is only 8 feet too.

Mike McCann
MMC Engineering

RE: Torsion on LVL beam supporting brick

(OP)
I don't understand how or where you would use the tension straps?

RE: Torsion on LVL beam supporting brick

Depending on the details of the section involved, the top of the beam wants to rotate outward from the structure with the torsion.  The tension link would come in restraining this top rotation with a connection to the top of the beam.

Mike McCann
MMC Engineering

RE: Torsion on LVL beam supporting brick

Mike's proposal to retrofit kickers would work structurally, but the overhead door is in the way.  I doubt you could get the kickers low enough on the beam to do much good.

I suppose installing a new column in the middle of the opening is out of the question?

 

RE: Torsion on LVL beam supporting brick

(OP)
Installing a column in the middle is absolutely out of the question. This is a 650k house. In fact, I am wondering if it would be even possible to replace altogether the existing beam for a new one. That certainly would involve some serious shoring...

RE: Torsion on LVL beam supporting brick

JAE-

The IRC also states that veneer above openings shall be supported by non-combustible materials (R703.7.3)

RE: Torsion on LVL beam supporting brick

As a semi-related point, the new version of ACI-530 got rid of that pesky 0.3" limit - its only L/600 now.   

RE: Torsion on LVL beam supporting brick

It looks like there could possibly be a large point load from the roof - maybe a girder truss if it is a trussed roof - at the center of the garage door header span.  Is the roof trussed, stick framed, or a mix?  The effect of any girder truss or point load may have been omitted on the header, especially if this structure did not have an original engineer involved in the design.

It is also interesting to note that a valley frames into the center of the span too.  Was this a sudden condition or gradual?  If sudden, was there a heavy snow that loaded the valley.

With that amount of brick above, the owner better seriously consider adding a central column to remedy the situation.  Should they ever try to sell the place with out a fix, they are going to take a much bigger hit if it is not fixed than nessing up the exterior look.  FUNCTION BEFORE FORM HERE - FOR SAFETY.

There were two 6.8 or higher earthquakes on the Western portion of the Pacific rim yesterday.  A 7.2 off the Kuril Islands, and a 6.8 near New Caledonia.  Is this structure in a high earthquake zone?   

Mike McCann
MMC Engineering

RE: Torsion on LVL beam supporting brick

(OP)
The structure is located in Georgia, so no snow to worry about. The condition most likely appeared gradually over approximately 3 years, as the crack were patched at first when the owner bought the house, and it seems cracks have reappeared after 3 years. We are in the process of having a contractor do an estimate of fixing the condition since this is in the middle of a buying inspection process.

The contractor will probably provide a high estimate since, as I told him, there is no engineering design done yet.

RE: Torsion on LVL beam supporting brick

OK.  

Then also check the end bearing on the header to the columns.  If this is a gradual condition, it could be crushing the bottom of the beam, causing the gradual cracking.  Torsional stresses may be the least of your problems here.

Mike McCann
MMC Engineering

RE: Torsion on LVL beam supporting brick

IceNine,

Yes - that's why you use a steel angle and ensure that there is a moisture barrier/separation between the exterior and wood beam - per LobstaEata's post (8th from the top).

 

RE: Torsion on LVL beam supporting brick

structurebeton,

Find out what the beam actually is before you go to the effort of thinking about replacing it. Drywall patching = cheap. You and the other people spinning their wheels speculating = expensive. When you find out the beam overstresses post that....also find out how the angle is connected (lags or thru-bolts?)  

RE: Torsion on LVL beam supporting brick

JAE-

The LVL is part of the lintel, and the code specifically calls for veneer above openings to be supported by non combustible lintels.

RE: Torsion on LVL beam supporting brick

IceNine,

I believe you are correct...I stand corrected.  Thanks.

 

RE: Torsion on LVL beam supporting brick

(OP)
So, it is then necessary to use a steel beam??? Then also use steel columns?  That seems a bit extreme...Are you sure about that restriction?

RE: Torsion on LVL beam supporting brick

IceNine

Take a look at Figure R703.7.2.2 above, showing masonry veneer being supported on a steel angle and fastened to wood studs.  The language contained in 703.7.3 (or at least a strict interpretation) seems to directly conflict with the associated figure on teh same page.  It would be interesting to contact someone at the ICC to obtain a clarification.

RE: Torsion on LVL beam supporting brick

This is an interesting thread that seems to be coming down to the other question of which code do you use (IBC or IRC). Keep in mind that steel design is not part of the IRC, so would you then be jumping to the IRC if you introduced steel...?? The provisions of the IBC Section 2304.12 are pretty clear about wood members supporting veneer.

I went to a introduction of the 2003 IBC/IRC back in the day and the code official explained that if "it" doesn't fit in the IRC, then use the IBC. I'd say that masonry veneer on a steel lintel fit better with the IBC. In which case I'd go with the Section 2304.12 which says wood supporting 4" veneer is a go.

 

RE: Torsion on LVL beam supporting brick

Sorry, I had a typ-o in my previous statement which should have read..."..jumping to the IBC...". Sorry for any confusion.

RE: Torsion on LVL beam supporting brick

I believe that if you have a minimum nominal 6X beam, it is a one hour fire rating without being wrapped.  If the studs shown in the detail mentioned above are wrapped with 1/2" gyp, then that is 1 hour too.  I do not really see the problem with the language and the detail in the field actual application here.

Mike McCann
MMC Engineering

RE: Torsion on LVL beam supporting brick

(OP)
I would think that either IBC or IRC apply, up to the engineer's judgement, to a residential house.

RE: Torsion on LVL beam supporting brick

bigmig-

2304.12 allows brick veneer to be supported by a wood foundation.

2104.1.6 rules out other uses, including lintels

 

RE: Torsion on LVL beam supporting brick

(OP)
So, are you all telling that it is necessary to use a steel beam to support a 18 ft span on a residential house, because there is brick veneer?

Any conclusions on this?

RE: Torsion on LVL beam supporting brick

If it's done moving maybe you just live with it.

If it's NOT done moving (i.e. a foundation issue) then you might spend $$ to fix with a nice heavy sttel beam only to have the crack open up all over again!  

RE: Torsion on LVL beam supporting brick

(OP)
The pattern of the cracking does not indicate a settlement problem.

RE: Torsion on LVL beam supporting brick

structurebeton

If you are designing strictly under the IRC, then it does appear that the LVL is a code violation (i.e. supporting masonry veneer over an opening per R703.7.3.)

The IRC does allow masonry to be supported by wood such as cases where an exterior wall turns back over a roof (per IRC Figure R703.7.2.1).  But it explicitly says no to wood beams supporting masonry over openings.

Since you have a wood beam supporting masonry in violation of the IRC, your next step would seem to be to go to the IBC in accordance with IRC R301.1.3 where it states that "Engineered design in accordance with the International Building Code is permitted for all buildings and stuctures, and parts thereof, included in the scope of this code."

So as an engineer, you can go to the IBC as structurebeton mentioned above.  So that then raises the question of whether wood beams can support masonry veneer in the IBC.

In the IBC - section 1405.5 indicates that masonry veneer must meet ACI 530.  Also, section 2304.12 states explicitly that no masonry may be supported by wood.

ACI 530, section 6.2.2.3.3 states the following: "Provide noncombustible lintes or supports attached to noncombustible framing over openings where anchored veneer is not self-supporting..."

So the wood beam is simply not code-compliant.

RE: Torsion on LVL beam supporting brick

I just looked at the photos, and I think we all may be going down the wrong path here.  I think these cracks have nothing to do with the deflection or torsional rotation of the lintel, but rather have to do with the fact that THERE ARE NO EXPANSION JOINTS IN ANY OF THE BRICK VENEER!!!  The brick has all kinds of openings, corners, etc., with no allowance for brick expansion.  Of course the hot Georgia sun is going to cause all of this veneer to expand, and it is cracking at openings and corners, where the brick is weakest.

I would recommend cutting in a vertical expansion joint on each side of the overhead door, filled with sealant and a backer rod.  I would consider adding a vertical EJ where the veneer steps up over the projection, to the left of the overhead door.  I wouldn't do anything with the lintel.

DaveAtkins

RE: Torsion on LVL beam supporting brick

(OP)
Even though the lack of control joint would have contributed to the cracking, the pattern of cracking (diagonal at the edges and vertical in the middle span) indicates to me a cracking due to excessive deflection.

What I am a bit concerned now is that apparently wood beam lintels are illegal. The contractor will have a fit, and generally speaking, because they haven't seen that on a house they will think that I am not a qualified engineer.

RE: Torsion on LVL beam supporting brick

What are the code provisions and are they are applied in your area?  Check with the contractor (or others) to determine if it's common practice in your area to support masonry with an LVL.

If this required a building permit, go take a look at the approved plans and compare them to what you have - bigmig is right, drywall is cheap, you need to know the existing conditions.  

The building code official will tell you if they allow it, you can ask their opinion about common practice and if they think it's acceptable.  Be somewhat obtuse, dont' identify your client or the house yet.

Please let us know how it turns out.

 

RE: Torsion on LVL beam supporting brick

I'd agree with diarmud on this.  The first thing you should do is contact the building department with this generic question - certainly there are many houses in your area with a garage and brick over the door.  Might be interesting to see what they say.

If they say LVL's are OK, then I'd also be interested in how they respond to the code logic I posted above.  It may be that the local code, as adopted, had amendments to the IRC that allow it but I wouldn't bet that would be true.

 

RE: Torsion on LVL beam supporting brick

I think there must be exceptions to the Code, because brick supported off wood lintels has been done here in Wisconsin, even on apartment buildings, which are governed by the IBC, not the UDC (Uniform Dwelling Code governs single family residences and duplexes here).  Is it possible that an LVL or PSL protected by GWB can be considered "noncombustible"?  I don't think so, but what the Code official thinks is what really matters.

I just find it hard to believe a steel lintel is required for your condition.

DaveAtkins

RE: Torsion on LVL beam supporting brick

I agree that the beam has deflected and causing those cracks. Since this occurrance has been a slow process as you noted, I guess the wood beam has gradually weakened with time. I am not an expert on wood, only speaking from my own experience with wood beams in my garage, have you considered jack-up the beam and strengthen it by adding steel facial plates if there is adequate space?  

RE: Torsion on LVL beam supporting brick

It's not that the wood has weakened with time, it's the process of increased humidity and drying throughout the year.  

A piece of wood, when wet with high humdity as in Georgia - 90 to 95% extended at times, then drying out with a decrease in humidity, will develop a memory of the deflection it has seen and will not return to the original shape.  This happens with varying load and varying humidity.  The same phenomenon is used to advantage in the construction of wicker furniture.  

This is not a problem that is going to go away on its own.  It will continue long term.  The installation of a steel beam would avoid this problem.

Mike McCann
MMC Engineering

RE: Torsion on LVL beam supporting brick

(OP)
Mike,
I believe they used an LVL or PSL to span 18 ft. However, I think it was not designed to suppport 1.5x dead load => Therefore, the beam has been subject to long term creep.  I think LVLs are less subject to humidity conditions, don't they?
Anyway, when they uncover the beam header, I will see the real story behind...

 

RE: Torsion on LVL beam supporting brick

I agree with DaveAtkins that there should have been vertical control joints.  But I think that the cracks are definitely due to deflection rather than temperature affects.

Some have said that it is common to have brick veneer over garage doors, but I think this instance is uncommon.  You have a two car garage with one single door, a roof valley coming in over the door, varying height veneer, a lot of things to go wrong.  The architectural design contributed a lot to this situation.

RE: Torsion on LVL beam supporting brick

hokie66, in your area of the world do they use wood beams to support concrete or masonry?  I know in some places there are very hard woods that may not be susceptible to the kinds of moisture concerns that compelled the IBC provisions here in the states.

 

RE: Torsion on LVL beam supporting brick

JAE,  I am not really up with the current housing code provisions here, as I don't do any small scale residential work.  I will post in the AS/NZS code issues forum and see if someone knows.  If not, I will check out the BCA (Building Code of Australia) soon and let you know.

I don't think there are provisions preventing concrete or masonry support on timber structures.  Certainly, there are a lot of existing examples, including lintels.  There are a lot of old brick buildings here with hardwood footings.  As long as the sapwood was removed and a durable species was used, they are generally still in good condition after 60 to 100 years.  One species, called ironbark for good reason, was commonly used.  Even the termites found it too hard.  Most housing here was built with hardwoods until recent years, but now plantation pine is the preferred material with house builders.  And now the termites are well fed.

Regardless of the supporting structure, it would be very uncommon here to use brick veneer over a double garage door.  Lightweight cladding is used.
  

RE: Torsion on LVL beam supporting brick

I don't know how others feel here, but I'll throw this thought out for discussion/consideration...

Could it be the INTENT of the IBC/IRC is that wood members not support STRUCTURAL concrete/masonry, but that brick VENEER supported by wood is allowed?  It seems to me that there is a difference.

True that falling brick veneer can kill, but that does not involve the structural failure of any main STRUCTURAL building component.  If so, it needs to be clarified.  If not, then maybe I'm reading more into the code than exists.  

Mike McCann
MMC Engineering

RE: Torsion on LVL beam supporting brick

Mike - the part in the IRC that denied masonry over openings was in a veneer section, I believe....I'm away from the office but I'll check on Monday.

 

RE: Torsion on LVL beam supporting brick

"Regardless of the supporting structure, it would be very uncommon here to use brick veneer over a double garage door."
In my experience (Aus, UK) no one would use timber to support brick veneer in a typical suburban home, especially over an 18' door.
Obviously it is more common in other parts of the world.

RE: Torsion on LVL beam supporting brick

This is why I wonder if a structural engineer was involved in the original design of the residence...

Mike McCann
MMC Engineering

RE: Torsion on LVL beam supporting brick

(OP)
Because the beam is failing, I very doubt a structural engineer was involved. In fact, very seldom a Structural engineer is involved in residential structures...

RE: Torsion on LVL beam supporting brick

(OP)
Here is the conclusion of this issue. Since I had given and estimate of between $5,000 and $ 30,000 to do the repairs, the seller had seek another opinion and got this second opinion, AFTER the sheetrock was pulled out:

....The 18-foot garage door opening is framed with a 3-ply 18" LVL. The beam is supporting the second floor
bonus room, roof and brick loads. There are cracks in the brick directly above the center of the door, along
the right side, and above the door on the left. Our calculations indicate that the 3-ply beam is slightly
overstressed to meet the brick deflection requirements of L/600. Furthermore, it is our understanding once
the brick was removed to verify bolting of the steel angle, it was discovered that at some locations the
vertical leg of the angle was not in direct contact with the beam, but rather compressible material. We
recommend that the compressible material be removed from behind the angle and the angle be bolted
directly to the beam. In addition, we recommend installing a 2-ply 16" LVL directly under the floor joists
spanning past the existing door header king studs. The new beam will carry the second floor load,
removing the load from the garage header....


So, there was 2 issues: Undersized Beam, And Compressible material between the angle and the beam...

This still does not resolve whether or not it is legal to use wood as a lintel beam.

 

RE: Torsion on LVL beam supporting brick

The IRC (2006,703.7) allows the use of wood members to support brick veneer provided the brick weighs less than 40 psf and deflection is limited to L/600 for total load and and is located in seismic zone A,B or C.

RE: Torsion on LVL beam supporting brick

weh:

R703.7.3 - veneer above openings shall be supported on lintels of non-combustible materials.

RE: Torsion on LVL beam supporting brick

(OP)
I tried to contact members of the ICC to discuss this IRC code contradiction, but apparently, the only way to talk to an ICC member (They are the ones that wrote the Building Code IRC) is by being a member!!!! For the moment I can't afford being a member of the ICC....

RE: Torsion on LVL beam supporting brick

Since the ledge angle is in contact with compressible material it will probably be necessary to needle beam the veneer and replace the angle with one that has a longer horizontal leg. Make sure the angle is galvanized because painted steel will start to rust in a few years.

If the building official will allow it, intumescent paint can be used to fireproof the LVL. If not PSLs are available with fire-retardant treatment.

Have you checked the deflection compatibility of 2-16" LVLs (I=1195) with 3 18" LVLs? (I=2552) There may be more load on the 18" LVLs especially since they are already preloaded with the dead load.  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources