Dear Folks,
I would like know the benefits, if UAT are connected at the terminals of GTGs (Gas turbine Generators ), instead of STGs (Steam Turbine G) in a combined cycle power plant.
Advanced Thanks...
 

RE: Unit Aux. Transformer (UAT)

Normally a unit auxiliary transformer provides power for the unit it is connected to, so the GT would have one UAT and the ST would have one UAT. You might consider that the GT is essential for operation of the ST, but not vice-versa.
  

----------------------------------
  
If we learn from our mistakes I'm getting a great education!
 

RE: Unit Aux. Transformer (UAT)

(OP)
One project has one GTG with HRSG, two STGs and two aux. boilers (coal based). In this case, which of the following options are better for feeding plant aux. loads
1. one UAT connected at GTG terminals + one UAT connected at STG terminals
(These UATs will feed unit loads as well as station loads)

2. one UAT connected at GTG terminals + One Station transformer
 

RE: Unit Aux. Transformer (UAT)

Impossible to say without seeing the single line diagram, but instinctively I would prefer a dedicated station auxiliary transformer given the choice.
  

----------------------------------
  
If we learn from our mistakes I'm getting a great education!
 

RE: Unit Aux. Transformer (UAT)

With just the information you provided, I'd go with option #2.  This way if STG-1 or it's GSU transformer is down for maintenance, STG-2 can run (assuming it gets it's power from the same UAT as STG-1).  Of course, option #2 looks like it will be a bit more expensive.

Is there a reason why there is no breaker between STG-2 and T20?

------------------------------------------------------------------------
If it is broken, fix it.  If it isn't broken, I'll soon fix that.

RE: Unit Aux. Transformer (UAT)

Hi.
From my point of view---> option#2 is better.

TurbineGen,
Good Q, but I would see it in another way:
or both steam turbine with GCB, or both w/o.
BTW, I think Kssschsekhar forgot delete GCB for the STG1 after revesion of option#1
Best Regards.
Slava

 

RE: Unit Aux. Transformer (UAT)

Option 2 looks the better solution operationally. The Station transformer will be more expensive than a second UAT, and it costs another bay in the HV substation but it is a worthwhile cost.

With a 3km line between the transformer and the HV sub I'd very much prefer to see a local GCB to protect the generator.
  

----------------------------------
  
If we learn from our mistakes I'm getting a great education!
 

RE: Unit Aux. Transformer (UAT)

Scotty.
I fully agree with you.
GCB is better from protection/operation/maintanance and synchronization point of view.
Best Regards.
Slava

RE: Unit Aux. Transformer (UAT)

(OP)
Thanks for discussion.
1. Yes, I forgot to delete the GCB for STG#1 in option-2. Good observation

2. With all your discussion, it seems reasonable to provide GCB at STG#2.  I would like to think more of it. Thanks for this.

3. As two boilers (coal based) are there in this project apart from HRSG, Steam turbines are not exclusively depending on GT .
As  both UATs in Option-1 will be sized for 2x100% plant load, still option-2 is recommended!!!

RE: Unit Aux. Transformer (UAT)

Hi.
I think if "Steam turbines are not exclusively depending on GT" , possible system w/o SAT. In case of GCB, possible feed plant load from the grid and after synchronazing generator.
In additional you wrote that size of every UAT enough for the whole plant load.
But in all cases a good style add GCB for the second STG.

Best Regards.
Slava

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources