Cable Bracing in Pre-Engineered Metal Buildings
For all of you pre-engineered metal building engineers out there (and others who care to weigh in) I would be interested in hearing your reasons for, or against, using cable bracing in lieu of rods or angles. I know there are many manufacturers who will not use them and even more that will. I am also interested in knowing whether or not those who do use cables are using a prestretched cable. I have been told by a cable supplier that all pre-engineered metal building manufacturers who use cable are using a non-prestretched cable. Is this accurate? Also, what limitations would you impose on the use of cables, i.e. crane buildings, seismically controlled structures, etc.? I would appreciate your perspective.
waytsh
waytsh
RE: Cable Bracing in Pre-Engineered Metal Buildings
For: They're cheap and have worked OK since ancient times (well, slight exaggeration).
Against: No clue other than situations for which the load is too high.
The cables are pulled tight, but I don't believe anybody actually measures the force either directly or indirectly. The analyses assume only the tension cables are effective, so there's no reason to try and figure out when some go slack.
There might be reasons to avoid them, but I'm not aware of any. Not claiming to be an expert, though, even though I've worked with MBs for a long time.
I'll say one thing, though: Beware being afraid of something just because you wouldn't use it in a conventional bldg. For example, I recently measured the web members of a 30K7 joist and some were something like 1" angles around 0.1" thick. A conventional bldg engineer wouldn't think of using that in a truss!
I do not have a problem using the cables for many applications where they are able to meet the deflection requirements of the building. The biggest problem I have is if they are not pre-stretched as described in ASCE 19-96 "Structural Applications of Steel Cables for Buildings". I believe they need to have this initial elongation taken out of them to "set" the final length of the cable and establish the minimum modulus of elasticity. Without doing this it becomes impossible to accurately calculate the longitudinal deflections of the building which is even more critical now with the 13th Edition of AISC.
I know you're thinking, "Well then just specify a pre-stretched cable." Unfortunately it appears from the suppliers that I have contacted so far that pre-stretching cables increases the cost to near that of rods thus eliminating one of the biggest benefits.
Do you know if the cables in the buildings you have looked at were pre-stretched?
That said, for a smallish (say 40'x100' building) cables probably work fine. Unfortunately, people want to stretch (pun intended) the limits and apply the same philosophy to 300' wide buildings where second-order becomes severe.
In answer to "asixth" we regularly do modular buildings over 300' wide. One of our engineers came to me the other day to discuss expansion joints in a proposed 650' x 2000' building. While certainly not a large percentage of our mix we have done quite a number of million square foot structures.
If you "heard" it on the internet, it's guilty until proven innocent. - DCS
http://www.eng-tips.com/supportus.cfm
Somehow these manufacturer's are justifying the use of even non-pre-stressed cables and I do not understand how. I have sent a question into MBMA to see if they have a position but seeing as how there is such a divide on the topic I doubt they will comment.
I'll let you know what I hear.