Ieff for composite steel beam
Can someone point me to a reference on how to calculate Ieff for a partially composite steel beam? I can't find anything in S&J or online except for a reference to BS 5950-3).
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
Ieff for composite steel beamIeff for composite steel beam(OP)
Red Flag SubmittedThank you for helping keep Eng-Tips Forums free from inappropriate posts. Reply To This ThreadPosting in the Eng-Tips forums is a member-only feature.Click Here to join Eng-Tips and talk with other members! |
ResourcesWhat is rapid injection molding? For engineers working with tight product design timelines, rapid injection molding can be a critical tool for prototyping and testing functional models. Download Now
The world has changed considerably since the 1980s, when CAD first started displacing drafting tables. Download Now
Prototyping has always been a critical part of product development. Download Now
As the cloud is increasingly adopted for product development, questions remain as to just how cloud software tools compare to on-premise solutions. Download Now
RE: Ieff for composite steel beam
Iequiv = Provided as equation C-I3-3 on p16.1-309 of 13th edition (incorrectly noted as Ieff).
For what it's worth, my mentor back in grad school is one of the big-name AISC guys and has been teaching steel for 40 years and he uses Eq. C-I3-3 in deflection calcs. Of course, that's the way I've been doing it for years too, but it's just because I followed his lead.
Also, to further muddy the water, Segui uses Ieff=0.75Itr in one of his example problems (Page 580 of the 4th Ed.).
That note about Iequiv is in the errata (I did look for that myself).
I noticed RAM also uses Ieff=Iequiv, not 0.75Iequiv. Also, my S&J text talks about using 0.33 to 0.5Ec when determining Itr to account for concrete creep and shrinkage.
I think Segui's method is clearly not correct because it totally leaves out the effect of more or fewer studs. Even ILB in Table 3-20 varies depending on Sum(Qn).