Folks,
I am trying to get a feel for the limits that you folks set for horizontal sweeps in unbonded cables on post-tensioned buildings.

Are there any published limits for how much the radius of a sweep can be for cables? I realize that more severe the sweep, greater are the losses. In addition, it leads to problems of occasional blowouts.

Architects love to offset columns as much as 8-10 feet over 30 foot spans etc, causing exaggerated sweeps. Do you guys have any limits on them?

Thanks

RE: PT Cables Horizontal Sweep

The minimum radii of curvature is given in "TESIT Post-Tensioning Systems" for various diameters of sheaths.  The friction coefficients increase with decreasing radius of curvature.  Empty ducts for supplementary tendons should be provided in case the friction losses are greater than expected.

RE: PT Cables Horizontal Sweep

(OP)
Thanks, but a quick google on TESIT does not give me any results. Any help?

RE: PT Cables Horizontal Sweep

A typical radius of curvature should be limited to 15-feet for 1/2" dia unbonded monostrand tendons. Reason being two fold, increased chance of blowouts as you had stated and secondly forcing a strand into a sharp curvature induces flexural stresses in the strand wires that may become significant if the curvature is extremely tight. This limitation is typically 20 times the strand diameter. The second stipulation controls the stresses in the strand while the first stipulation controls the stresses in the concrete. I have worked for 2 post-tension suppliers in the past and have typically maintained a 15-foot radius. Sharper curvature is possible; however you should place hairpins within the curve to minimize the horizontal pressure on the concrete. The PTI manual would be a good resource.

Regards,

AUCE98
 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources