How to convert 4 wire input to 2 wire?
Need your help folks.
I need to bring 4-20 signal from 4 wire current transmitter to 2 wire input card (Delta V). It was surprise for me that in Delta V i have to use a pair of cards for the same field signals. What are the options?
BB
RE: How to convert 4 wire input to 2 wire?
A signal isolator is used. Action Instruments, Moore Industries, and Phoenix Contact are among the manufacturers that provide these.
xnuke
"Live and act within the limit of your knowledge and keep expanding it to the limit of your life." Ayn Rand, Atlas Shrugged.
Please see FAQ731-376: Eng-Tips.com Forum Policies for tips on how to make the best use of Eng-Tips.
The module is the same, it's the termination unit that is different. You may be able to connect your 4 wire device
+ to the even pin - to the bussed power supply negative. You can easily check this out by measuring the resistance across these 2 points. If it's 250 Ohms you are in business.
I have attached a schematic of the 2 types.
Roy
Thanks a lot!
That's what I was looking for. Hope I will be able to deal with these microscopic  terminals and power termination of the carreer.
BB
The Bussed power terminals are the large ones at top of rack
Roy
