Load Bank connections

Load Bank connections

Load Bank connections

(OP)
We have a generator that needs to be load bank tested. The output is 480V 3P 1000A. The test will be limited to 800A and we are installing a separate 1000A circuit breaker in an I-line panel to go to the load bank.

The methods I have seen so far for hooking up a rented load bank is to connect 4/0 welding cable into a circuit breaker with the panel exposed for the duration of the test. It works but violates a number of safety regulations. I want to use a panel of Cam-lok lugs (E1017 series) and have the contractor plug his 2 sets of 4/0 cables. According to to what I find in the NEC I need 700MCM cables for use in a raceway/conduit. My problem is I don't have room left in the panel for 700MCM cables. Is there a legal justification for using 4/0 cable for a short run, <6 feet, to the cam-lok lugs or perhaps a better method?

RE: Load Bank connections

If the breaker is 1000 A, you need (at least)1000 A ampacity in the conductors, regardless of length.  



 

RE: Load Bank connections

700MCM is very large diameter cable, diffcult to handle and terminate. The breaker may not even accept 700MCM cables.

You may want to use multiple 4/0 "welding" cables. Check the ampacity of those cables in free air.

As for safety, you need to take necessary precautions and limit access to the test area during the test. Keep safe distance from energized components. Are you a contractor or desing engineer?

 

RE: Load Bank connections

Under the Canadian Code welding cable must be rated at 60 degrees. That puts 4/0 at 300 Amps in free air and 195 Amps in the panel. Probably why the panels are left open.
Try 4 x 250 MCM RW75 per phase.

Bill
--------------------
"Why not the best?"
Jimmy Carter

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources