Cooling load - Rule of thumb
Cooling load - Rule of thumb
(OP)
At HVAC Equations, Data & Rule of thumb book:
Commercial Offices = 300 to 400 sq.ft./ ton , does it apply to all ambient condition , like Middle East region? I think no. Does anyone know other region factor?
Commercial Offices = 300 to 400 sq.ft./ ton , does it apply to all ambient condition , like Middle East region? I think no. Does anyone know other region factor?





RE: Cooling load - Rule of thumb
Persian Gulf is only the most humid place in the world
If your ventilation air is included in those rules of thumb you could be in trouble you could be 100 Btu per CFM of fresh air
I am in a humid environment and 300 to 400 sqaure feet per ton would mean a sparsely populated office, like a person for every 300 to 400 square feet, so 1/4 to 1/3 the amount of office equipment you would expect, 1/4 to 1/3 the ventialtion load you would expect
Take the "V" out of HVAC and you are left with a HAC(k) job.
RE: Cooling load - Rule of thumb
Good luck.
RE: Cooling load - Rule of thumb
Paul G.