Carrier 50HJ, 5 ton
Carrier 50HJ, 5 ton
Carrier 50HJ, 5 ton
I need constant 1125 cfm of outdoor air does any one know or familiar with Carrier Weathermast 50HJ 5 ton unit?  This is a brand new unit.  The problem is overpressurization, which is what I am afraid of.  If a system has an air economiser then it has to have a mean to relief excess air into the evironment without recirculation.  Can anyone goes further into this problem.  I don't know if this unit comes equip with power exhaust or not.  All this factory components good enough to remove excess air?
RE: Carrier 50HJ, 5 ton
Before applying a power a power exhaust application, you need to look at the complete system. Can you provide the design basis of the system, such as total system flow, indoor & outdoor conditions, coil loads and other exhaust flows?  A HAP load would be proper way to apply the unit. 1125 CFM on a 5 ton HJ is over 50% of the nominal flow. At this high % of OA to RTN flow, it will tax the DX performance. The evaporator is not designed for high latent loads. High OA % flow may cause problems with the heating section too.  Hopefully, you are not trying to use this in a 100% OA application. Is the 1125 CFM a flow fixed 100% of the time? What are you thoughts on controls and temperature /humidity requirements?
If the system application is correct, Carrier offers a couple of options for the unit that can be installed in the field. If you are being driven solely by pressure issues, then I would apply the micrometal fully modulating version rather than the end switch fixed volume.
In addition to the above, if the above unit came with an economizer, then it is c/w barometric relief. (Power exhaust would be a field-installed accessory).