Concrete Pour Rate Schedules
|
Concrete Pour Rate SchedulesConcrete Pour Rate Schedules(OP)
Do formwork suppliers typically provide concrete pour rate schedules on the formwork shop drawings?
Red Flag SubmittedThank you for helping keep Eng-Tips Forums free from inappropriate posts. Reply To This ThreadPosting in the Eng-Tips forums is a member-only feature.Click Here to join Eng-Tips and talk with other members! |
ResourcesWhat is rapid injection molding? For engineers working with tight product design timelines, rapid injection molding can be a critical tool for prototyping and testing functional models. Download Now
The world has changed considerably since the 1980s, when CAD first started displacing drafting tables. Download Now
Prototyping has always been a critical part of product development. Download Now
As the cloud is increasingly adopted for product development, questions remain as to just how cloud software tools compare to on-premise solutions. Download Now
|
RE: Concrete Pour Rate Schedules
Check the current edition of the ACI Standard for the Recommended Practice for Concrete Formwork (ACI 347-78, or later). Lots of good info here as to what should be communicated, depending on the situation.
Mike McCann
MMC Engineering
RE: Concrete Pour Rate Schedules
RE: Concrete Pour Rate Schedules
If I remember correctly, the few times I've seen drawings from a supplier (probably EFCO or Dayton) they gave the pour rate and either gave or referenced the mix design.
RE: Concrete Pour Rate Schedules
RE: Concrete Pour Rate Schedules
gwynn,
In your experiences with designing formwork and reviewing formwork, have you ever warned or seen warnings about slump exceeding 7" and its impact on pour rates?
Also, would you mind telling me what company you work for? If you don't want to share that information, that is fine. I am just trying to figure out if pour rate schedules are industry standard on concrete column form shop drawings and knowing a couple of firms that do this would help.
Thanks!
RE: Concrete Pour Rate Schedules
Dik
CONCRETE FORMWORK
MATERIAL FOR CONCRETE FORMWORK SHALL CONFORM TO WITH THE CURRENT EDITION OF CSA O86.1, CSA O121, CSA O151 AND CSA O177
PLYWOOD FOR FORMWORK SHALL BE [EQUIVALENT TO COFI COFIFORM-PLUS | COFIFORM-PLUS | AINSWORTH POURFORM 107] AND SHALL BE GRADE STAMPED ACCORDINGLY
FORMWORK DESIGN DEFLECTION HAS BEEN LIMITED TO L / 180 WHERE L IS THE SPAN OF THE SUPPORTING FORMWORK ELEMENT. WET SERVICE CONDITIONS HAVE BEEN ASSUMED FOR FORMPLY DESIGN. SHORT TERM LOADING CONDITIONS HAVE BEEN ASSUMED FOR ALL FORMWORK ELEMENTS
MATERIAL FOR STUDS SHALL BE EQUIVALENT TO SPECIES S-P-F, GRADED #2 OR BETTER AND SHALL BE GRADE STAMPED ACCORDINGLY
MATERIAL FOR WALES SHALL BE EQUIVALENT TO SPECIES S-P-F, GRADED #2 OR BETTER AND SHALL BE GRADE STAMPED ACCORDINGLY
FORMWORK DESIGN PRESSURES ARE IN ACCORDANCE WITH THE CURRENT EDITION OF ACI 347. FOR FORMWORK LESS THAN [15FT | 5.0M] HIGH, THE MAXIMUM PRESSURE IS Cw x Cc x [150 + 9000 * R / T] AND FOR FORMWORK GREATER THAN [15FT | 5.0M] HIGH THE MAXIMUM PRESSURE IS Cw x Cc x [150 + 43400 / T + 2800 * R / T], WHERE R = RATE OF DEPOSITION AND T = TEMPERATURE. THE MINIMUM DESIGN PRESSURE OF 600 PSF HAS BEEN WAIVED TO COMPLY WITH CANADIAN PRACTICE
FORMWORK DESIGN PRESSURES ARE IN ACCORDANCE WITH THE RECOMMENDATIONS OF THE COFI WHICH ARE BASED ON THE CURRENT EDITION OF ACI 347. THE MAXIMUM PRESSURE, FOR A RATE OF PLACEMENT LESS THAN 2 METRES PER HOUR, IS 7.2 + 785 * R / (T + 17.8) , WHERE R = RATE OF DEPOSITION IN METRES PER HOUR AND T = TEMPERATURE IN DEGREES CELSIUS. THE MINIMUM DESIGN PRESSURE OF 600 PSF HAS BEEN WAIVED TO COMPLY WITH CANADIAN PRACTICE
THE CHEMICAL COEFFICIENT (Cc) HAS BEEN ASSUMED TO BE 1.2; CONCRETE SHALL BE TYPE 10, 20 OR 30 WITH A MAXIMUM OF 40% FLY ASH
THE CHEMICAL COEFFICIENT (Cc) HAS BEEN WAIVED TO COMPLY WITH CANADIAN PRACTICE
THE UNIT WEIGHT COEFFICIENT (Cw) HAS BEEN ASSUMED TO BE 1.0 FOR NORMAL WEIGHT CONCRETE
THE UNIT WEIGHT COEFFICIENT (Cw) HAS BEEN WAIVED TO COMPLY WITH CANADIAN PRACTICE
CONCRETE RETARDERS SHALL NOT BE USED
MAXIMUM HEIGHT OF FORMWORK SHALL NOT EXCEED [15FT | 5.0M] UNLESS NOTED
LIMITATIONS ON THE HEIGHT OF FORMWORK HAS BEEN WAIVED TO COMPLY WITH CANADIAN PRACTICE
MAXIMUM RATE OF POUR SHALL NOT EXCEED [7FT | 2.1M] PER HOUR
MAXIMUM CONCRETE TEMPERATURE SHALL NOT EXCEED 20 DEGREES CELCIUS
CONCRETE DENSITY SHALL NOT EXCEED [150PCF | 2400KN]
MECHANICAL VIBRATION SHALL BE LIMITED TO THE TOP [4FT | 1.2M] OF THE CONCRETE POUR
RE: Concrete Pour Rate Schedules
RE: Concrete Pour Rate Schedules
Dik