arrester failures
2

arrester failures

arrester failures

(OP)
We experienced failure of the arresters I mentioned in thread238-213060: Lightning arrestor short circuit rating. The utility feeding this switchgear is 4800V ungrounded with about 21kA sym available. The circuits are from a common substation bus, ungrounded, and do not have recloser operation. I selected an intermediate class polymer 6kV gapless MOV arrester, rated 40KA pressure relief. Their 10kA, 8/20 crest voltage is 16.7kV. They are installed in separate compartments in metal-enclosed interrupter switchgear, rated 15kV.

This is a main-tie-main setup with the arresters in separate back-to-back compartments. The side was blown out of the C-phase arrester on main #2. About 15 minutes later there was a fault in the arrester compartment protecting main#1 and its C-phase arrester was destroyed. I can't tell if the origin of the second fault was internal to the arrester or external. There was considerable arcing in both arrester compartments, but I don't know exactly when it occurred. Fuses on both mains were found blown, but again I don't know exactly when. The utility reported a ground fault for roughly the time interval between our two events.

The utility engineers and local electricians are suggesting a higher voltage rating. The arresters protect oil-insulated transformers rated 60kV BIL that are about 50 feet away.

Any thoughts on changing the arresters to 9 or 10kV ? Any other thoughts on the failures or replacement arresters type selection?

RE: arrester failures

alehman,

If I have understood your post correctly,

1)Is 6 kV=MOV of the said arresters?
2)How did you install arresters with MOV=6 kV for a 15 kV ungrounded system?

 

RE: arrester failures

(OP)
1. Yes. 6kV arresters.
2. The system is 4.8kV ungrounded. The switchgear is rated 15kV.

Thanks,

RE: arrester failures

I'm assuming the 6 kV is probably a duty cycle rating.  The corresponding MCOV would be 5.1 kV.

With voltage regulation, the voltage could be higher than nominal.  5.1/4.8 gives you 1.0625 pu, so you could tolerate up to 6.25% higher voltage.

The polymer arrester failure description with the side blown out sounds like an overvoltage failure.  The polymer housing usually splits and you get a power arc external to the blocks.

I'd be inclined to replace it with a 9 kV duty cycle rating (MCOV is 7.65 kV).

The protection characteristics would be roughly 1.5 times the 16.7 kV or 25.1 kV.  I estimated this based on the ratio of the arrester ratings (9/6).  Even if the surge doubles, you have almost the required 20% margin.

RE: arrester failures

(OP)
Yes, 5.1kV MCOV. This was as initially recommended by the manufacturer, the utility engineer, and as recommended by IEEE 62.22.

The utility states they maintain +-5% voltage. They are trying to obtain their substation voltage recorder data for the time leading up to the event.
 

RE: arrester failures

I would not be inclined to change the arrester to 9kV. This is for higher system voltage and would continue to be guided by IEEE 62.11 table 1. I need to ask some questions though and the answer should point to the problem.

What is the BIL of the entire system? is this more, less than or equal to the arrester BIL?

What is the ground resistance at the point where the arrester is grounded?
 

RE: arrester failures

opmgr1
It's good to have noble preferences but you're not offering alehman any alternative.  Leaving a 6 kV rating in will probably destroy more arresters.

Sure the 9 kV rating is for higher voltage systems, but it will work.  You're sacrificing some protective margin, but you should be OK.

System BIL - line should be higher than the transformer and other equipment (if any) should have their own arresters.

I'm not sure the ground resistance would change anything if we're dealing with a sustained overvoltage issue.

RE: arrester failures

(OP)
opmgr1,
Switchgear is 95kV BIL (except for the 6kV arresters), cables are 15kV 133% EPR, transformers are 60kV BIL. There is an extensive grounding system, but I do not know the resistance.

My thought process was that the normal line-ground voltage should be significantly <4.8kV since the utility does not allow ground faults to persist.

A 9kV arrester in the same product line would have 25.0kV 10kA/8x20 crest.

RE: arrester failures

Magoo,
I dont agree with your post. If the problem is one of sustained over-voltage The approach is to find out what is causing the overvoltage (temporary or sustained) and fix that, not putting bandage on the situation by increasing the arrester duty cycle rating.

Alehman, looking at your post re L-G voltage are you saying that this system is an un-grounded wye system and that the C-phase to ground voltage is close to 4.8kV?

RE: arrester failures

(OP)
The system is 4.8kV nominal, ungrounded. I don't know the actual voltages, except at the secondary of my DY transf's.

RE: arrester failures

I would look for the source/cause of the overvoltages first and correct that. Switching transients/ Lightning/resonance??

9KV MOV may help if the source and mangitude of OV is known such as switccing transient below the ratig of the MOV. On the other hand it may cause greater damage (when operates) or mask something you do not want to mask, if the source of OV is per say restriking ground fault/resonance.

 

RE: arrester failures

Is this a wye or delta connected system?

RE: arrester failures

Wouldn't referencing one phase of an ungrounded system to ground cause all phase to neutral connected equipment to see line to line voltage?  

RE: arrester failures

Correction: The phase to neutral equipment connected on the phases not referenced to ground would experience line to line voltage. The next ground fault (overvoltage of the arrester) would result in a phase to phase fault. Arcing could result in a 3phase fault and explain your blown fuses. Just a thought.  

RE: arrester failures

(OP)
opmgr,
The utility refers to their service as 4.8kV delta.

mxgxk,
I've gone through several scenarios as to the sequence in my mind. Personnel at the facility reported two audible explosions. After the first explosion loads fed from main#2 were de-energized and there was considerable smoke coming out of the switchgear (I don't know the status of the fuses at that point). The utility says the ground fault current is about 2 to 3 amps. I wouldn't think that would be enough to explain the audible explosion. One possible scenario is there was arcing phase-to-phase after the first failure and one or two fuses blew, leaving a ground fault.

Then after about 15 minutes, there was a 2nd explosion and the remaining loads were off. This could have been caused by the arrester on the 2nd service failing or an external flash-over on the arrester due to residue from the first fault.

RE: arrester failures

For a system sourced by a delta, arresters should be applied with an MCOV greater than the line to line voltage. Otherwise, a ground on any phase (no fault current will flow) will subject the arresters (connected phase to neutral) to line to line voltage. The arresters will fail rather quickly if misapplied.

RE: arrester failures

MxGxK
The present arresters are applied with an MCOV greater than the line-to-line voltage, but it could be close.

alehman
How much cable are you dealing with between the utility sub and the switchgear?  I could envision the utility regulating around 4800 V +/-5% at the sub, but with enough cable, you'll get voltage rise at light load that will raise the voltage unless the regulators/LTC have line drop compensation.  So you could be at the ragged edge as far as the 5.1 kV MCOV.

With a ground fault, 2 of the phases will see this overvoltage, as MxGxK points out.  From the utility perspective, they might not detect this condition unless they have special relaying since it really doesn't draw much fault current, only some cable charging current.  With it undetected, it will subject the 2 unfaulted phases and their arresters to a damaging level of overvoltage.

Maybe alehman can see if I'm off base with these assumptions.  Also do you have sensitive ground fault detection in the switchgear or it is just set to alarm?  This should help better define the problem.  

RE: arrester failures

magoo2 nailed it!

Quote:

"The utility says the ground fault current is about 2 to 3 amps. I wouldn't think that would be enough to explain the audible explosion. One possible scenario is there was arcing phase-to-phase after the first failure and one or two fuses blew, leaving a ground fault.
No matter how many times you replace your arresters, you will get more arresters damaged until you solve the problem of arcing L-G faults in your system. 2 to 3 amps is a typical charging current of ungrounded 4.8kV systems. With the system capacitance highly charged, the threshold voltage could have been reached; re-strikes occurred 'till the arresters gave way!
Try reviewing your line protection and see if you can use the option to trip if L-G fault occurs and not just alarm. Broken-delta ground fault sensing can help.
My 2 cents!

RE: arrester failures

(OP)
Our switchgear is manually operated fused switches with no other protection options available. The ground fault sensing I mentioned is the utility's and located at their substation. I don't know any specifics on their relay.

I see your point about voltage regulation. Our secondary voltage runs a few percent high, but I need to verify the transformer tap settings.

I'm still waiting on voltage logs from the utility, but they have said there were no other recent ground fault events.

RE: arrester failures

These ungrounded systems are succeptable to ferroresonant over voltage, overvoltage (as much as 1.73pu rise) as a result of earth fault transient overvoltage, and overvoltage as a result of switching switching (whether deliberate or as a result of protection from faults). If there is upstream switching as much as 10pu overvoltage burst can occur which stress the insulation of the arrester resulting in failure. Of course it is much cheaper to replace the arrester than the equipment that it is protecting.
Note if there is a transient fault there can be a build up of high voltages (up to 6 times nominal). This high transient voltage can initiate a second fault at the weakest insulation point resulting in failure. For this scenario you definately do not want to increase the duty cycle rating of the arrester. As one poster hinted at you may want to invest in SEF protection if this is a financially viable option or it may be cheaper to replace arresters.

RE: arrester failures

Embarrassing. I should have read the post more carefully.

RE: arrester failures

Nothing to be embarrassed about!

 

RE: arrester failures

(OP)
I appreciate all the feedback.

opmgr1, by "duty cycle rating" you mean voltage rating?

Any thoughts on the pressure relief rating? We had some damage to the switchgear as a result of this failure. I am concerned about possible future failures causing more extensive damage.

RE: arrester failures

Yes, Voltage rating of the arrester. What type of damage(s) did the switch gear sustained?
Anything from the utility regarding the EF?


 

RE: arrester failures

(OP)
Damage was due to arcing that occurred and residue. One cubicle door was blown open and bent. Arcing damage to barriers and doors. Nothing yet from the utility.

RE: arrester failures

For a station class arrester you may want to go with pressure relief of 80kA min. Look through the hubbell arrester catalogue for additional info.


 

RE: arrester failures

How would the utility measure the ground fault current on a floating system?

 

RE: arrester failures

Quote (LionelHutz):

How would the utility measure the ground fault current on a floating system?
A Zero Sequence CT can detect the difference (current passing to the ground). Normally, the vector sum of the three phase currents is zero. ZCT does not register current. With ground faults, additional current on the grounded phase, though highly capacitive, appears in the ZCT.

RE: arrester failures

Quote:

A Zero Sequence CT can detect the difference (current passing to the ground). Normally, the vector sum of the three phase currents is zero. ZCT does not register current. With ground faults, additional current on the grounded phase, though highly capacitive, appears in the ZCT.

What is the current path from ground back to the transformer side of the CT?? Capacitive coupling in the transformer??

If so, that seems like a very poor ground fault detection scheme to me.
 

RE: arrester failures

LionelHutz,
You're probably right! I did have a problem with coordinating ground fault relays with this kind of setup before. The catch is that when you supervise the earth fault trip circuit by a contact from an undervoltage relay taking pickup from a broken delta PT, you can set the EF very low and still detect the ground fault.

RE: arrester failures

(OP)
The utility finally reports that there were no recorded anomalies leading up to our failures. So the arresters are going back to the manufacturer for analysis.

RE: arrester failures

With no recorded anomalies, I assume this rules out ferroresonance, resonance, switching transients and lightning.

I suspect the arrester manufacturer will tell you the arresters saw a TOV condition which exceeded their capability, but let's wait for their response.

Don't let the utility off the hook at this point. They just told you there was nothing that they were doing that was coincident with or just prior to the arrester failures.  They still have some useful info that you should get out of them.
- how high did the substation voltage get in the month or so prior to the failures?
- what time of day did they have the highest voltage?
- if you happen to have a just a single-phase to ground fault (SLGF), will the utility relays be able to sense it or is it below their radar screen?  This is a critical piece of info.


From your perspective,
- can you calc how much distance and what size 15 kV cable there is between the substation and your switchgear?
- is it just an underground feed from the substation or is there some overhead distribution too in the mix of things?
- what time of day did the failures occur?
- was your load high or low at the time of arrester failure?

I'm still entertaining the possibility that you'd get enough cable rise that you could be close to the MCOV - but this theory requires that you also have a SLGF.

We recently had some termination failures in an arrester cabinet because of the way the incoming cables were arranged in the cabinet.  They were almost horizontal and this put the grounded end of 2 terminations close to the adjacent phase.  The result was one of the terminations flashed to ground and 2 arresters failed.  The initial report was an outage due to arrester failures.  On closer examination, we found that the terminations on the incoming cables should have been vertically arranged and no fault would have occurred.  These terminations were only a few months old.

There's still a chance to get some additional info from the utility.  I'd go after it.

  

RE: arrester failures

(OP)
Magoo,
Responding to your questions based on what I currently know...

They said the voltage has been very stable, with some daily variance up to 123 to 124V. Yes, they can detect SLG faults and did see our first fault as an SLG for about 15 minutes.

I may be able to get a rough idea of the distance, but I don't have the utility's maps. They say there's no overhead except bus at the substation. Load was probably on the low side, but there's not much variation.

I think there's a possibility the 2nd failure was a flashover perhaps due to fallout from the first event, but it also appears at that time there may have been a SLG fault resulting from the first event.

We'll pursue additional info from the utility, but I'm doubtful of learning anything meaningful. They have offered to install a power quality analyzer on our transf secondaries, but there wouldn't be any ground reference since they are DY.

Thanks again...

RE: arrester failures

I would not pressure the utility too much on this, being a utility person myself you may find that you ran into a dead-end and there is no information from them to support the theory of an over-voltage. The fact of the matter is that based on the exposure of the lines, utility customers will be subjected to voltage sags and swells.
Alehman, I would still explore specifying a minimum pressure relief of 80kA without modifying the arrester duty cycle.
 

RE: arrester failures

(OP)
The manufacturer examined the arresters and said (as I suspected), that one on each service failed internally and the others sustained external arcing damage. They said that the arresters were "misapplied", in spite of the fact that they were selected for the system voltage in accordance with their published literature.

Alan
----
"It's always fun to do the impossible." - Walt Disney

RE: arrester failures

Is the utility quoting you the substation regulated output voltage?  Does your utility service transformer have primary taps and if so where are they set?  If you said so I missed it, but do you monitor incoming voltage?

I have seen improperly rated arresters fail on 3 wire systems from extended ground faults and the time it will take to failure is proportional to the amount of overvoltage.  Appears you are on the edge of the envelope with rated MCOV depending on the actual service voltage.

You could very likely have 6+ percent over nominal voltage on the service.

It is certainly something to investigate, but agree with the other posts with respect to sacrificing protection at the higher ratings....but if it is the arresters already causing failures, it is obviously time up upgrade.

Alan

Democracy is two wolves and a sheep deciding what to have for dinner.  Liberty is a well armed sheep!
Ben Franklin

RE: arrester failures

(OP)
The utility was quoting substation bus voltage. Voltage at our transformer secondaries is also about +3% with on-nominal tap. I have no primary meter.

The arrester manufacturer and switchgear manufacturer have recommended increasing the voltage rating of the arrester. My inclination is to increase the voltage rating to 9kV and the withstand to 80kA.  

Alan
----
"It's always fun to do the impossible." - Walt Disney

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources