Backpressure correction for balanced bellows
We have 2 identical balanced bellows type PSVs. PSV A is set at 9.5 barg and PSV B 10 barg. They both protect the same equipment which has a 10 barg design pressure.
PSV A has a 16% overpressure, PSV B has 10% overpressure. Each PSV has a backpressure of 4 barg.
When I refer to API 520, Figure 30, Kb factors for A and B are 0.95 and 0.87 respectively.
Thus, even though A and B are identical valves with same relieving pressure (11 barg), the de-rating due to backpressure is less for valve A. Therefore, A is predicted to have greater capacity than B.
This doesn't make sense to me. Can anyone confirm whether this logic is correct?
RE: Backpressure correction for balanced bellows
steveb1111, I did not check the numbers, but think your logic is correct.
I assume your backpressure is built-up plus superimposed.  The extra capacity for valve A will result in a higher backpressure and thus a lower Kb.  It is somewhat of a trial-and-error procedure. (I'm not saying that they will equal out, but the Kb's should get close to each other.)
It's the the builtup plus superimposed backpressure. We don't find that much of a balancing out effect. Valve A has slightly higher backpressure, but this is more than compensted for by the difference in Kb.
The 16% overpressure valve with the lower set point has around 8-10% more capacity which I don't understand. This difference results in valve A having adequate capacity, but B is undersized. The answer to which appears to be reduce the set point of B to 9.5 barg.
If your backpressures are approximately equal, I guess the capacities are different.  It may have something to do with the mechanical design of the valve internals.  I'd give it the old "consult valve manufacturer" routine.
PRV A with lower set pressure will have lower spring force. When PRV A lifted, with same relieving pressure, it tends to open slightly more to allow larger flow.
The PRV B may not be undersized if it can take half the relieving flow.
JoeWong
Chemical & Process Technology