Does any API or other standard decree or recommend a fire fighting system for a diesel fuel oil tank located at a power station but remote from the main plant.
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
Firefighting for fuel oil tanks
|
RE: Firefighting for fuel oil tanks
I suggest that you review the requirements of NFPA-30.
Be mindful that the low flash point of most fuel oils controls the degree of fire prevention systems required.
Also, be aware of the NFPA-30 tank spacing rules that address minimum distances to buildings and structures that are "normally occupied"
-MJC