in what situation do we use three pole CB for DC?

RE: 3 pole CB

The poles are wired in series for greater voltage interrupting ability, mostly but not always for inductive loads.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: 3 pole CB

Discuss this with the manufacturer to determine what ratings are available for this arrangement.

RE: 3 pole CB

Bill has it.  DC requires much greater/faster contact separation than the equivalent AC circuit.  By connecting the circuit breaker contacts in series you achieve this.

Keith Cress
kcress - http://www.flaminsystems.com

RE: 3 pole CB

Bill is correct.  Since the DC has no zero crossing voltage there must be a greater gap to extinguish the arc.  Be advised, however, a vacuum interrupter may not be suitable for this application depending on the voltage and current.

------------------------------------------------------------------------
If it is broken, fix it.  If it isn't broken, I'll soon fix that.

RE: 3 pole CB

2
It is also a matter of how the breakrers are listed.  Many 3-pole AC breakers are Listed (after testing by UL or such) for DC use. Many 1P and 2P MCCBs are also listed for DC use, typically in smaller ratings.

In higher ratings, the 3rd pole comes handy for the reasons mentioned above. More importantly no special breaker has to be manufactured, it is basically an AC breaker tested and listed for DC use. Most of 3P breakers are listed in certain wiring configuraiton showing which poles will be seriesed.

See for example:
http://ecatalog.squared.com/pubs/Circuit%20Protection/Molded%20Case%20Circuit%20Breakers/Thermal%20Magnetic%20Molded%20Case%20Circuit%20Breakers/0601DB0401.pdf

 

RE: 3 pole CB

(OP)
Thanks all for yr valuable coments..
but i m still confused that why dc require much greater contact separtion?how can u achive by connecting CB contacts in series?

RE: 3 pole CB

AC nicely provides a current zero 100 or 120 times per second, DC never does.  If one contact opens 1/4 inch (made up number) then three contacts in series provide 3/4 inch of air gap, three times the dielectric strength to interrupt the current that doesn't want to be interrupted.

RE: 3 pole CB

Ditto Rbulsara statement above..

We use Cutler Hammer brand MCCBs, that specficly lists the series connection configuration to increase the interrupt rating.

These MCCBs are used as the EPO shunt tripped disconnect in the battery feed path in our customer 48V DC power plants..

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources