Backflow Prevention Large Diameter Storm Sewer

Backflow Prevention Large Diameter Storm Sewer

Backflow Prevention Large Diameter Storm Sewer

(OP)
Need information on available backwater valves for 15" RCP storm water drain that runs into tidal canal. Also appreciate advice on where to install valve -- outlet? in-line? 15" RCP line pitches approx. 4"/100ft. x 300ft total run.

RE: Backflow Prevention Large Diameter Storm Sewer

.... or tideflex

www.tideflex.com

RE: Backflow Prevention Large Diameter Storm Sewer

(OP)
Good advice -- Thanks! Local engineer is proposing Tideflex TF-1; and that will work at the outlet into the tidal canal.

RE: Backflow Prevention Large Diameter Storm Sewer

We have implemented Tideflex valves in a number of our projects.  In our local, flap valves tend to get obstructed with debris and fail to close.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources