AC vs DC coil on large starters

AC vs DC coil on large starters

AC vs DC coil on large starters

(OP)
Looking for some feed back on why you would spec out a DC coil or AC coil on a large motor starter (size 5 or 6).  I'm old school and back in my day we used DC to avoid vibrational issues associated with AC coil.  Don't know if this is still a valid consideration or not.  Your opinons will be greatly appreciated.

RE: AC vs DC coil on large starters

This is generally a design standard of the starter manufacturer.  I would let them provide their standard design, whatever it happens to be.  Starters with dc coils will come with their own rectifier, so it's completely transparent to the end user.  DC coils will generally draw less current when pulled in, so are commonly used at Size 4 and above.

The vibration angle is a new one on me.  
 

RE: AC vs DC coil on large starters

DC coils also generally hold in better under voltage drop conditions, something you are more likely to encounter the larger the motor gets. dpc is right, most larger starters have DC coils even if they are labeled as AC, they just have the rectifier built-in.


"If I had eight hours to chop down a tree, I'd spend six sharpening my axe." -- Abraham Lincoln  
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies  

RE: AC vs DC coil on large starters

Be aware that some DC units are dual coil.  That is there is a second coil for extra pull in power and this disconnects when pulled in.  These extra contacts are potentially a source for failure.

RE: AC vs DC coil on large starters

I wondered, because DC coils normally draw far more power pulled-in than equivalent AC coils.

Keith Cress
kcress - http://www.flaminsystems.com

RE: AC vs DC coil on large starters

There are also contactors with a little rectifier + switcher and a controller that makes the coil draw a heavy current for the pull-in and then reduces current considerably for holding the armature.

Those contactors do not chatter or drop out when the line is going low during a heavy start.

Gunnar Englund
www.gke.org
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...

RE: AC vs DC coil on large starters

Normally it is not wise to spec a contactor coil as AC or DC. You will just eliminate a lot of good equipment from your list of choices.
The contactor manufacturer will choose the coil in the design process and will not change the design for one sale.
The exception would be where your favorite contactor had a DC coil where all others used AC in that size. Spec'ing a coil type that is only available from one maker will effectively steer the selection to your favorite. This is probably not ethical but it is done.

Bill
--------------------
"Why not the best?"
Jimmy Carter

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources