Atex Motor Classification
I am requesting a cross reference for motor classification as follows: Class I Division II Gas Group C,D T3. What would be the Proper Atex rating for the aforementioned classification. Is it imperative that I know the gas or can this be determined with the rating listed above?
RE: Atex Motor Classification
If we learn from our mistakes I'm getting a great education!
http://w
If I well understood the equivalence may be as follows:
Class I div.2 C T3 = 3 G EEX de II B T3
Class I div.2 D T3 = 3 G EEX de II A T3
The Canadian Electrical code has a cross reference table.
You have to know the gas.
Some group C gasses are group II A and some are group II B.
Some group D gasses are group II A and some are group II B.
Bill
"Why not the best?"
Jimmy Carter