Inverse Time Undervoltage Formula
3

Inverse Time Undervoltage Formula

Inverse Time Undervoltage Formula

(OP)
Guys, this may be a dumb question to make but I would appreciate if you will provide me a better understanding.

A G.E. Manual states that its undervoltage delay settings defines the family of curves shown below:

T = D / [1-(V/Vpickup)]

where T = operating time
      D = Undervoltage Delay Setting
          (D = 0 operates instantaneously)
      V = secondary voltage applied to the relay
Vpickup = Pickup Level

Looking at the sample graph, for D = 2 and %voltage pickup of 2%, the operating time is approximately 2 seconds. I'm a little confused on what values I would use for V and Vpickup to coincide with the graph below:

[IMG]http://i532.photobucket.com/albums/ee327/primo_beltran/Inverse_time_UV_curve.jpg[/IMG]

My application is for a 120VAC secondary and with a target operating time of 3 seconds...what will be the Delay setting (D)?

  

RE: Inverse Time Undervoltage Formula

3s at what %Vpickup? D=5 is too long, but D=1 and 2 intersect 3s at different %Vpickups. Both are faster than your target at 2%.

Since Vpickup is expressed as a percentage in the graph, V=100% (of 120V) in the formula above.

RE: Inverse Time Undervoltage Formula

(OP)
Hi stevenal,

Its 85% nominal volts (120VAC) for 3 seconds.

RE: Inverse Time Undervoltage Formula

Depending on the relay, (you may be able to set the time dial to 1/2) I don't think that's going to happen.  You would need to set the relay for a time dial of 1/2 to get a 3 second response at 85%.  (85% of 120 = 102 volts.  The time dial of 1 hits 3 seconds at 65% or 78 volts.  

RE: Inverse Time Undervoltage Formula

None of the curves shown hit that point. Shortest is D=1 at about 7s.

RE: Inverse Time Undervoltage Formula

(OP)
In a secondary selective switchgear, the client specs calls for 0.85P.U. U/V pickup for 2 seconds and initiate the transfer.

Is it acceptable to set a 0.85P.U. voltage pickup using a DEFINITE time of 2 seconds instead of using an inverse voltage curve?

RE: Inverse Time Undervoltage Formula

IMHO - A definite time delay might be better in this application.  If a momentary voltage dip occurs to say 10%V for a few cycles, do you want to transfer immediately or give the system 2 seconds to come back on its own? The inverse time curves will intitate transfer faster than the two seconds specified for low voltages.

RE: Inverse Time Undervoltage Formula

yes, I agree 2, Happy Christ's mass

RE: Inverse Time Undervoltage Formula

Nightfox.
Pay attention on the RCWilson recommendation.
I agree 3.
Best Regards.
Slava

RE: Inverse Time Undervoltage Formula

(OP)
Thank you very much for all the technical assistance. We will get the settings on now.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources