Hallo guys,
I have a scheme whereby the neutral of a 23MVA 33/11kV trafo has only one neutral CT (BUSHING) of class X. The incomer breaker too has class X CTs. I want to use ICT to be able to use the single bushing CT for both SBEF and REF.

Is it safe to use the ICT or is the REF alone sufficient for protection of the Trafo windings and the cable to the incomer breaker.

RE: REF/STAND BY EARTH FAULT

The REF and SBEF are two separate protection functions. The REF will protect the transformer winding and the cables to the breaker. SBEF is standby earth fault protection. It is backup protection in case of uncleared faults out on the network, or earth faults outside the REF zone. It may also protect the neutral earthing resistor if there is one, and may act as a cheap busbar protection system by tripping the LV bus section first and the transformer LV C/B second. Do you really want to compromise important backup protection for the cost of a neutral CT? You have the option to get another CT fitted in the bushing, or if there is a neutral cable terminated on the bushing you could install a slipover CT on the cable, or in the NER cable box. Lots of possibilities, and not very expensive.
Regards
Marmite

RE: REF/STAND BY EARTH FAULT

Horrible idea.

The SBEF CT doesn't need to be anything special and you should have enough adjustment on the relay to allow a fair choice of CT ratio. Are you saying that you can't find any CT at all? If you have an NER then you could use a metering CT as the CT will never see high current under fault conditions.
  

----------------------------------
  
If we learn from our mistakes I'm getting a great education!
 

RE: REF/STAND BY EARTH FAULT

Apprenteng.
I'm not sure if it's  a good idea use series connection for the REF function. It not seems.  Are the REF HI or LI?
Actually, you have a solidly trafo grounding..
REF is good function, but not must here. 87T is enough sensetive in such confuguration. You can use REF no problem and SBEF with residual connection. In first case you can add neutral CT and reconnect SBEF relay.
Just opinion.
Best Regards.
Slava.
BTW, why PUNGLU is name of drw, one of our members is PUNGLU smile.

RE: REF/STAND BY EARTH FAULT

thanks everyone
i would like to point the following:

1. REF is used because 87T doesn't cover 100% of Xfmr winding.
2. if the REF is high impedance type, deticated CTs shall be used for this function.

Best Regards
SMB

RE: REF/STAND BY EARTH FAULT

(OP)
Thank you guys for the advice. Sorry, the trafo should be YNyn0 with the LV side solidly grounded. Punglu? Draw attention to him... Had similar configuration in a previuos thread. May be draw attention.

RE: REF/STAND BY EARTH FAULT

(OP)
REF is high impedance

RE: REF/STAND BY EARTH FAULT

NO, you must dedicated CT for HI REF protection
Best Regards.
Slava

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources