Moment along a rebar lap splice
A cantilevered retaining wall that I am designing has vertical bars, lapped with vertical footing dowels. The wall height from top of footing is 8-feet. There are footing dowels (#4 @ 9") which extend from the footing, 3-feet into the wall. They are lapped with vertical wall reinforcing (#4 @ 18") which is 8-feet long; therefore, the lap is 3 feet at the bottom of the wall.
The footing dowels are designed for the moment at the top of the footing. The vertical reinforcing bars are designed for the moment at the top of footing dowels - at the 3-foot height. But the moment changes pretty rapidly along the length of the lap, because it is a cantilevered retaining wall.
How do I know that I don't have a development deficiency at any particular cross section along the lap?
RE: Moment along a rebar lap splice
Mike McCann
MMC Engineering
DaveAtkins
Thank you both for your input.
DaveAtkins
Randomly check required reinforcing at two locations, say 1' and 2' above the footing. For each location, calculate the reinforcing required and make sure the reinforcing ratio is maintained wthin the range of one development length above this specific location/plane. Done.
But, in any event this is better than a linear moment diagram, in terms of development of reinforcing.
DaveAtkins
Now you can create a reinforcing force diagram and compare
Experience can be gained either by open discussion, or self persuasion, depending on the nature of the topic in concern. For this case, I think a quick calculation may provide better understanding and strengthen your conviction for other matters that share the similarities. Have fun.
Mike McCann
MMC Engineering
JSA2, I think you need to carefully consider your design.
In cantilever retaining wall design, the dowels coming out of your footing, serve one purpose and one purpose only. That purpose is to transfer the moment from your wall, to your footing. The wall itself, basically creates a vertical force couple. Tension in the steel pulling out of the footing, compression in the concrete pushing into the footing. Never the less, it should transfer the moment into the footing. Most of us turn the bend of the dowel into the toe of the footing. These dowels should have a Class B lap splice (1.3ld) into the wall, and be fully developed in your footing.
The primary reinforcing in your footing should be in the top portion of your footing on the heel side. If reinforcing is needed on the toe side, it should be in the bottom portion of your footing (which is why most of us turn our dowels that way).
If a key is required, the vertical reinforcing should be placed towards the toe of the wall.
I say all of this because your original post doesn't make sense. Hopefully, your footing is thicker than your wall. I can't figure out why you would need reinforcing @ 9" in your footing, and @ 18" in your wall. It doesn't add up. As others have stated, don't make it by such a gnat's behind. There are very few times where I have spaced reinforcing greater than 12".
The lap is 3-feet and it is at the bottom of the wall. The dowels are designed for the wall moment at the top of footing. The wall verts are designed for the moment at the top of the lap (3-feet above top of footing). The footing dowels are a greater area of steel, say per lineal foot of wall than the the verts.
As you imagine the moment increasing below the top of the lap, the bars which are there to resist this increasing moment (the footing dowels) are not yet developed. But the moment is increasing in what has been described here as a concave cubic shape. My inquiry was for the purpose of understanding whether I only had to check the reinf quantity at the top and bottom of the lap, or if there could be a critical, governing section somewhere along the lap.
The bar termination has always been the tough part of solving this problem in my experience.
In my copy of ACI 318 (don't ask what year) it appears you should check article 12.10.
Good Luck
I understand what you are trying to do, but, I think you are going around it from not quite the right angle. I'll try to explain but as you already know, it can get confusing.
You're trying to treat it as a stepped wall, w/ your step being three feet from top of footing. When you do this, you have to lap the reinforcing at the step. If the wall was being formed in two pours, the first of which is 3 feet from the footing, and your design shows that at this location, you need #4@18, then every other one of your #4@9 dowels have to extend out from the top of that 3' pour, whatever length is required (I think around 30" for f'c=4000).
Does that make sense?
The #4@18" bars in discussion satisfy both strength & development requirements for the plane at 3' above the footing. Similarily the #4@9" bars satisfy both for the plane at the wall-footing interface. Now let's check the plane at 2' above the footing, in which the amount of reinforcing lies in between #4@9" & #4@18". By inspection, the #4@18 bars are still ok, since it has 2' length below this plane. However, the #4@9" dowells, while meeting strength requirement, apparently do not satisfy the development length requirement (3'-2' = 1' too short), a further check using ACI "Excessive Reinforcement" provision is required to justify the shortcoming (note that the #4@18" bars do not meeting strength requirement at this plane while meeting development length requirement).
You may check the plane at 1' above footing, for which both #4@18" & #4@9" are ok by inspection. If I didn't make any mistake in example provided, your reinforcing plan obviously is questionable.
I didn't link anything in my discussion.
I think you can upload certain types of document throuh the link provided by this forum located at the very bottom of this page (next to "Step 3 - Attachment"). I have not tried so far.
For your question in this post, you can simply draw 4 horiz. lines representing elevation 0', 1' 2' 3' above the footing. Then draw 2 vertical lines at a distance apart - one for #4@18" extended from top of wall to top of footing, and one for #4@9" dowells that are terminated at 3' above footing (ignore the splices). Now exam each bar at 2' level, and ask the question "Does each bar passing this plane satisfys both strength and development criteria in both directions"? Well, simple question can be quite confusing, in fact it is really not that simple if you chose to think about. Again, have fun, and nice weekend.
I am correct. Pull out your reinforced concrete text book and study lap splices. You're developing the bars (dowels) going into your footing, to transfer the moment into your footing, therefore, your vertical reinforcing in your wall should match your dowel spacing. If you do not understand this, seek your senior engineer's advisement.
Kslee1000's post confirms what I'm telling you. He is describing the theory behind it.
Ugh!! I did not use the "F" word!
I have not "run this to ground" by checking the moments verses the laps at a few different sections along the lap length yet. My sense so far is that the development of both bars of the lap, when added together will be adequate for the increasing moment at any cross section along the lap. If I do this computation, I will come back to post my results. Thanks again for everyone who contributed to this.
Only a personal opinion, your walls will not fail if it (splice) is the only item deviated from code requirement. However, it could be one of the reasonS that contribute to a failed wall.