We have (2)10MVA 15kV-4160V transformers that feed essential load of about 9 MVA. There is an independent 13.8kV system on the site.
To increase the reliability, it would be to our advantage replace one of the 15kV feeders and feed from the 13.8kV system.
Instead of buying a new transformer, I wonder if it is feasible to get an autotranformer that could bump the voltage from 13.8kV to 15kV and re-use one of the existing tranformers? Any problems?
To increase the reliability, it would be to our advantage replace one of the 15kV feeders and feed from the 13.8kV system.
Instead of buying a new transformer, I wonder if it is feasible to get an autotranformer that could bump the voltage from 13.8kV to 15kV and re-use one of the existing tranformers? Any problems?






RE: Autotranformers on 13.8kV or 15kV systems
If the existing transformers have taps, which they probably do, you might want to look at that option as well.
A standard transformer would have two 2.5% taps above and below the nominal voltage. 95% of 15 kV is 14.25 kV, is only 103.3% of 13.8 kV. So this might work for you, especially in an emergency condition.
RE: Autotranformers on 13.8kV or 15kV systems
RE: Autotranformers on 13.8kV or 15kV systems
You'd have to see if the available short circuit current exceeds the capability of the voltage regulator. Other than that, a 333 kVA regulator is a standard rating.
Otherwise, the straight autotransformer would work.