I have contracted to design a six-story apartment building, in California. This is larger than any of my previous jobs (custom homes). I am trying to determine what materials/structural systems I am permitted to use, but surprise, I can't figure out the 2006 IBC...
The building is a six-story, sixty-five foot tall rectangle.
I want to use steel moment frames at the lowest floor, and wood framing/shearwalls above. Will this be permitted?
Table 503 of the code seems to say that, no, this is not permitted.
Table 12.2-1 of ASCE 7-05 seems to sat that, yes I am permitted.
Can anyone help me sort this out? I realize that I may not be able to build five stories of wood framing, simply for design/strength reasons, but I'll figure that out as I work on it. I just need to know if it is, in general, permitted.
The building is a six-story, sixty-five foot tall rectangle.
I want to use steel moment frames at the lowest floor, and wood framing/shearwalls above. Will this be permitted?
Table 503 of the code seems to say that, no, this is not permitted.
Table 12.2-1 of ASCE 7-05 seems to sat that, yes I am permitted.
Can anyone help me sort this out? I realize that I may not be able to build five stories of wood framing, simply for design/strength reasons, but I'll figure that out as I work on it. I just need to know if it is, in general, permitted.






RE: maximum building height for type V construction
per table 601 the structural frame would need a 2 or 3 hour fire protection; roof beams & joists would need 1 to 1.5 hour fire protection.
see attached. the construction type column tells you want kinds of materials you can use
RE: maximum building height for type V construction
RE: maximum building height for type V construction
Remember, that is My opinion, I might be wrong.Let's see what others say.
Best of Lucks
Rarebug
RE: maximum building height for type V construction
J
RE: maximum building height for type V construction
RE: maximum building height for type V construction
Table 503 is pretty clear - R-2 is limited to 2 or 3 stories for Type V, and 4 stories for IV, III, and II. You can add an additional story if the building is fully sprinklered per NFPA 13, per 504.2. NFPA 13R does not permit the stories to be increased beyond 4.
Sprinklered or not, it appears the building must be constructed of Type I, which will be a protected structure.
Since you are limited to combustible construction, ASCE 7's allowing combustible materials would not be permitted in a 6 story building.
Don Phillips