There is a note in remarks section (Turn down is 50%)in fin-fan cooler
There is a note in remarks section (Turn down is 50%)in fin-fan cooler
(OP)
There is a note in remarks section (Turn down is 50%)in fin-fan cooler specs.Can somebody explain what does it mean.





RE: There is a note in remarks section (Turn down is 50%)in fin-fan cooler
50% means that you can lower the heat load on the cooler by 50% and still operate.
RE: There is a note in remarks section (Turn down is 50%)in fin-fan cooler
Well this is a two bay air-coolers, my point is this 50% turn down is more related to fan or fan motor or flow of fluid control to lower the heat load. I would appreciate if you can clarify.
RE: There is a note in remarks section (Turn down is 50%)in fin-fan cooler
Regards,
Mike
RE: There is a note in remarks section (Turn down is 50%)in fin-fan cooler
1. Start and stop fans. Most bays have two fans with one being a two speed and one being a single speed.
2. Change the two speed fan from high to low or low to high speed.
3. Automatic controls using inlet and outlet louvers to limit the air flow through the fan.
4. Automatic controls using recirculation louvers that redirect some of the outgoing air back to the incoming side. This limits the heat transfer while keeping the steam coils from freezing up.
5. Automatic controls using variable speed drives on the fan motors. This is probably more common at other plants. We use this method rarely.
It is not common to limit the process flow rate or bypass process flow around the cooler. This is used more often on shell and tube exchangers using cooling water since pinching on the cooling water has an undesirable affect on water-side fouling.
Johnny Pellin
RE: There is a note in remarks section (Turn down is 50%)in fin-fan cooler
rmw