Smart questions
Smart answers
Smart people
Join Eng-Tips Forums
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS

Member Login




Remember Me
Forgot Password?
Join Us!

Come Join Us!

Are you an
Engineering professional?
Join Eng-Tips now!
  • Talk With Other Members
  • Be Notified Of Responses
    To Your Posts
  • Keyword Search
  • One-Click Access To Your
    Favorite Forums
  • Automated Signatures
    On Your Posts
  • Best Of All, It's Free!

Join Eng-Tips
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail.

Posting Guidelines

Promoting, selling, recruiting, coursework and thesis posting is forbidden.
Jobs from Indeed

Link To This Forum!

Partner Button
Add Stickiness To Your Site By Linking To This Professionally Managed Technical Forum.
Just copy and paste the
code below into your site.

ruready (Structural) (OP)
11 Dec 08 13:08
What category do surchages fall under in the IBC load combinations?  If you have a strip surcharge from a building, do you split the dead and live loads up or would the resulting load applied to the retaining wall be H?  IBC 1610.1 "Design lateral pressure from surcharge loads shall be added to the lateral earth pressure load" is interepretd in our office two ways, any surcharge load is classified as H or make sure you include it in your design in combination with H. Thanks
garrettk (Geotechnical)
12 Dec 08 10:58
What is the allowable bearing pressure of the footing nearest the wall?  Without digging through the code, that seems to be the logical surcharge load that should be appled to your retaiing wall.

You'll need your geotech to come up with the resulting horizontal and vertical pressures.
InDepth (Structural)
15 Dec 08 15:59
I agree with garettk, use the bearing pressure as soil surcharge load (good practice and allows for future demo of adjacent building and redevelopment).

**********
Here is my take on your question:

1. If you are transmitting any load (DL, LL, EQ) through a soil medium to another structure it should be considered a soil load.
2. If you are transmitting a load by underpinning, then the appropriate load is used and transferred to the wall.

If you are using ASD load combos, it really doesn't matter. If you are trying to use LRFD or have a seismic load, then you need to decide how to tackle the situation. You have to think about probability....the 1.6 on H in LRFD is provided because of the uncertainty involved in soils. You can't use 1.2 load factor of a DL surcharge in soil because there isn't that level of certainty.

One item you need to verify is if the building is imposing a seismic surcharge on the permanent structure.

In the load combos, I define "H" as 3 Cases
Case 1: H = Lateral Soil Load + Building Surcharge + Soil Seismic Increment.
Case 2: H = Lateral Soil Load + Construction Surcharge
Case 3: H = Lateral Soil Load + Traffic Surcharge

Notes: Case 1 - beware of seismic directionality arguments and resistances (and seismic return periods....for temporary shoring, use much less)
Case 2 & 3 - Add Building Surcharge if in the zone of influence. All Cases: Ground Water pressure is included in H.

The geotech will probably give you a Bousinnesq surcharge pressure, but beware that this is usually a "rigid" wall distribution that should be reduced per NAVFAC DM recommendations.

You may Also want to consult ASCE 37-02 and AASHTO for further guidance.
 

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close