Electrical Conduit in CMU walls

Electrical Conduit in CMU walls

Electrical Conduit in CMU walls

(OP)
Where can I find information regarding the effects of electrical conduit inside structural CMU walls?  A contractor wishes to run the conduit horizontally in the wall, which would obviously cross through the grouted cells.  They also want to place vertical conduit in cores that are to be reinforced and grouted.  Is this acceptable practice?

RE: Electrical Conduit in CMU walls

Aluminum conduit - NO!!!!!!!!!!!!!

PVC OK, but ask for his placing plan and make him stick to it.   

Mike McCann
MMC Engineering

RE: Electrical Conduit in CMU walls

(OP)
It is metal conduit, but I don't believe it's aluminum.  We have already told them that they could not place vertical conduit in the walls.  I just want to know for future reference. Is there a problem running it horizontally or vertically in the walls as long as it's not aluminum or not in contact with the rebar?  Would the voids created by the conduit through the cores weaken the prism strength of the CMU wall?

RE: Electrical Conduit in CMU walls

It is done all the time, except, I would have them place it in ungrouted vertical cores. Comply with requirements in ACI 530.

RE: Electrical Conduit in CMU walls

I wouldn't have a problem with pvc or galvanized conduit vertically, whether in grouted cells or not.  Horizontally, it can be a concern depending on your stress conditions and the conduit size.

RE: Electrical Conduit in CMU walls

The rigid metal conduit has an equal or greater strength than the grout that it displaces and may be used in any orientation with good consolidation.

RE: Electrical Conduit in CMU walls

Very interesting reply civilperson. What about pvc?

I don't see any reason that the conduits need to be in the vertical cores which are to be grouted.

RE: Electrical Conduit in CMU walls

If you have vertical runs of conduit to decrease the amount of hotizontal runs, that make good sense.

If you have good engineering and resulting open cores, the only logical thing is to put the conduit in the open cores from a practical constructabilty standpoint and also for cost. Puting conduit in a grouted cell with rebar only decreases the structural liability. Doubtful if you have any cores that are grouted without reinforcement in them.

Dick

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources