Please help me to find some references about substation falut calculation. 34.5kV Ring Bus (9 bus) with 3 Transformer, 60 mva of each. Thanks a lot
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
Substation Fault Calculation
|
RE: Substation Fault Calculation
RE: Substation Fault Calculation
RE: Substation Fault Calculation
Ex. 1500 3phase pad, 480Y/277, with 5.75% IMP.
(((((1500*1000)/3)/480)*1.732)*100)/5.75=31377 Fault Current
Hope this helps
Trent
RE: Substation Fault Calculation
1. Impedances of the three transformers.
2. Equivalent short circuit impedance of the system connected to the primary of the transformers.
3. Impedance of any series reactors (if any).
4. Are the three transformers operated in parallel on the secondary side?
RE: Substation Fault Calculation
www.eazypower.com.
Thanks again.
RE: Substation Fault Calculation